Thanks Brent!!! I will use it,it fits perfect for my purpose.
Ignacio GomisGomis
This sort of issue is one of the uses for the EnergyManagementSystem:InternalVariable object. There is an internal variable available called ?Pump Maximum Mass Flow Rate? that can provide the result of the autosize value for each pump.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Nacho Gomis
Sent: Thursday, January 24, 2013 8:29 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] EMS Mass Flow Rate
Hello group,
I'm trying to generate a default idf to be simulated with several weathers. This IDF contains an EMS to override the condenser flow rate, I set an variable flow rate. So my EMS sets the flow rate depending on my own rules.
The problem now it is I have a successful IDF for one weather, running without errors but this model doesn't have any autosize field for the pumps, I have filled all the autosize fields.
When I try to set, for example the Rated Flow Rate, to autosize I would need to reference my minimun flow rate, which is set in my EMS code, with a value from a EnergyPlus sensor. For exaple the 10% of the nominal flow rate.
Could someone help me with this issue?
P.S.: I have attached the working IDF and its weather.
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___