Check your outdoor specification and your outdoor air controller. If you have set the outdoor air controller to deliver a minimum amount of outdoor air to the space at all times, the system will always be delivering air, and therefore always pumping in air at the deck temp. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, HJ  wrote:
>
> Thanks for your advice. I didnt set a setpoint for humidity and I think 
> the outdoor air is not humid for certain period but the system is still on.
> 
> I suspect the VAV is turned on because it tried to meet the deck 
> setpoint temperature which is 12.6 C. However, I am not sure how should 
> I change this. There is reheat before supply air entering each zone.
> 
> HJ
> 
> 
> On 2/8/2013 2:30 PM, luke_dorna wrote:
> >
> > It could also be that you are supplying outdoor air and dehumidifying it.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > , HJ wrote:
> > >
> > > Hi all,
> > >
> > > I notice the VAV system is still running even if room T is way below
> > > setpoint T (e.g. at night ,Tsetpoint is 26, Troom is 22 something).
> > > However, CAV system does not have this type of problem. Since I am
> > > modeling hybrid ventilation, I would like the VAV system shut down when
> > > Troom meets Tset. Is there a way to achieve that?
> > >
> > > Thanks,
> > >
> > > HJ
> > >
> >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/