[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: schedule on the fresh air rate of a CAV, possible ?
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: schedule on the fresh air rate of a CAV, possible ?
- From: "FrancescoP" <direzionecontraria@xxxxxxxx>
- Date: Wed, 13 Feb 2013 10:59:10 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 13 Feb 2013 03:59:17 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1360753156; bh=8KLw4euzN0CCZ1BOtsnDZASdS/Ac0NiGbMgGBTaM+PA=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=C8GeHMzKgg9BW42xIsQdO9UIXsKWZFoxzG+/n7OpblcmwOYmxjElElJNtmOZO31aKa1ASLsII7RZdXVRjZK0PUefbcfhENNjNksPEcXn2j1HuBMaZ4yiiO4211yiGC8amAuVpsxiT9qMZUxLrjJnP3loKxOuM62tL19DEujG5rg=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=iGEEitmxU2puTQDaBPnIMscPVEKxuJ478gzX743/pd3haFld34URxqCssGGoSNJkksDnR7GKJJhB1sqlL6P1jQojPEG44DUVRxyPcb7aNprfZTpgjDu/4RaKctUCAxGjTnOy7fnKOdObl/37WaHs+RG8R7XiVLbNDZk+HLOJd0Y=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
I did in the following way:
Controller:OutdoorAir,
1primo_ufficionord Unitary HP AirToAir/1 Outdoor Air Controller, !- Name
1primo_ufficionord Unitary HP AirToAir/1 Relief Air Outlet, !- Relief Air Outlet Node Name
1primo_ufficionord Unitary HP AirToAir/1 Extract Fan Air Outlet Node, !- Return Air Node Name
1primo_ufficionord Unitary HP AirToAir/1 Mixed Air Outlet, !- Mixed Air Node Name
1primo_ufficionord Unitary HP AirToAir/1 Outdoor Air Inlet, !- Actuator Node Name
0.036, !- Minimum Outdoor Air Flow Rate {m3/s}
0.036, !- Maximum Outdoor Air Flow Rate {m3/s}
NoEconomizer, !- Economizer Control Type
ModulateFlow, !- Economizer Control Action Type
, !- Economizer Maximum Limit Dry-Bulb Temperature {C}
, !- Economizer Maximum Limit Enthalpy {J/kg}
, !- Economizer Maximum Limit Dewpoint Temperature {C}
, !- Electronic Enthalpy Limit Curve Name
, !- Economizer Minimum Limit Dry-Bulb Temperature {C}
NoLockout, !- Lockout Type
FixedMinimum, !- Minimum Limit Type
occupazione, !- Minimum Outdoor Air Schedule Name
, !- Minimum Fraction of Outdoor Air Schedule Name
, !- Maximum Fraction of Outdoor Air Schedule Name
, !- Mechanical Ventilation Controller Name
, !- Time of Day Economizer Control Schedule Name
No, !- High Humidity Control
1primo:Ufficionord, !- Humidistat Control Zone Name
1, !- High Humidity Outdoor Air Flow Ratio
No, !- Control High Indoor Humidity Based on Outdoor Humidity Ratio
BypassWhenWithinEconomizerLimits; !- Heat Recovery Bypass Control Type
Schedule:Compact,
occupazione, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays SummerDesignDay WinterDesignDay, !- Field 2
Until: 08:00, 0, !- Field 4
Until: 18:00, 1, !- Field 6
Until: 24:00, 0, !- Field 8
For: Weekends, !- Field 9
Until: 24:00, 0, !- Field 11
For: AllOtherDays, !- Field 12
Until: 24:00, 0; !- Field 14
As output:variable you can check "AirLoopHVAC Actual Outdoor Air Fraction"
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Geert Bellens" wrote:
>
> I want to put a schedule on the fresh air rate of a 100% fresh air CAV system. The zones have all different air rates depending on the time of the day varying between 20 and 100%. I have the impression that this is not possible...?
>
> I I use a VAV, the air rates are controlled by the indoor temperature, which is not what I want.
>
> Geert
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/