[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Infiltration
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Infiltration
- From: "FrancescoP" <direzionecontraria@xxxxxxxx>
- Date: Wed, 13 Feb 2013 10:51:55 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 13 Feb 2013 03:52:00 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1360752719; bh=TZtkbRxtVDTfZz5fZ8Bx6kbaLSyMMLwGLxw+FXv4bU8=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=YieLbP4ZMDZGfXBnh+zY78m8nsHrhVND/H/KidYJ8bgg7fldNY2uUnSIrn2E+uHDn8esTUDzGg2xOvll23pxqwey5aZZlET/pzB5iePhjG1cR5mC3GxIT8dHdZ0zI7+jk+FwAybOQpPCWn9GtALmc9G9q9gNDf2BNC4UWCrpdFA=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=Yq8L6edruHBJwM2h2qTqWOLRG+4bw7i+7mvyQ4oxeGRSvNYZ3vUmmwFY8vm32TG4q45tdr6c9x6MbNPP+ibmQMTLLcW/2cx9lwL01CgBVu1a308X8bScdHGeFomQ/eKvhsWeGauY6BqVzbUHuM2A3x4ZPDnsQsyZ6hS/qv41+vU=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Very interesting, Jean. I have not understood some aspects.
You divided by the "Air Mass Flow Exponent When Window or Door Is Closed". Why? I mean, I don't know what equation you referred to.
In order to get "kg/s @ 1Pa per m crack" why didn't you divide by the total length of the cracks?
What object of EnergyPlus did you use to implement the results?
Best Regards
Francesco
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" wrote:
>
> I'm interested in this subject. I once setup manually the air tightness in the following way:
>
> e.g.
> Infiltration of closed exterior windows/doors is set for a relatively tightly sealed building at 0.3 ACH at 50Pa Blower Door. This is achieved by taking the building volume 2057 m³ at 0.3 ACH = 617.1 m³/h = 0.171466 m³/s divided equally over the number of exterior window/door cracks,
>
> i.e. Baseline Building has 119 exterior window/door x4 cracks each (top, bottom, side, side) ï? crack Air Mass Flow Coefficient When Window or Door Is Closed (kg/s @ 1Pa per m crack) = ((0.171466)/(119x4))/((50)(0.5) ) = 0.00005092852413
>
> where Air Mass Flow Exponent When Window or Door Is Closed (dimensionless) = 0.5
>
> Interior doors are modeled as always closed with (both baseline and design models) the crack Air Mass Flow Coefficient When Window or Door Is Closed (kg/s @ 1Pa per m crack) = (0.024[1])/ (4 cracks x (25)(0.65) ) = 0.000725
>
> [1] Poulsen, P.E. â??Smoke Control Doors Test Reportâ?? Danish Nat Inst for Testing of Materials, Copenhagen (1979)
>
> All edges
> Avg Gap Thickness mm = 0.6 mm
> Gap Depth = 60 mm
> Gap Length = 6.0 m
> Flow Rate = 0.024 m³/s
>
> Cracks are not modeled for non-openable interior windows.
> Holes are assumed to have Air Mass Flow Coefficient (kg/s @ 1Pa per m crack) = 0.1 and Air Mass Flow Exponent (dimensionless) = 1.0 for free flow without resistance.
>
> ....................this was a simple 29 room one story building.
>
> I have not checked the latest from designbuilder for the n50 proceedure and natural ventilation, but am looking forward to in the future.
>
> Jean
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jeremiah Crossett wrote:
> >
> > Thanks Ned-
> > You might check how this feature works when natural ventilation is set to
> > calculated and scheduled-- It would make since that when calculated is
> > checked the AFN infiltration objects are used on all external surfaces but
> > when scheduled is checked than infiltration is modeled
> > ZoneInfiltrationDesignFlowRate..
> > *
> > *
> > *
> > *
> > *Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions*
> > *
> > 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> > www.phasechange.com
> > *
> >
> > *
> > *
> > *
> > *
> >
> >
> >
> > On Fri, Feb 1, 2013 at 10:40 AM, Edward G. Lyon wrote:
> >
> > > **
> > >
> > >
> > > Thanks, we have Design Builder in the company, but I don�t use it
> > > myself. When I have some time I�ll check out what they do exactly.****
> > >
> > > ** **
> > >
> > > *Ned Lyon, P.E. (MA, WV)**
> > > *Staff Consultant ****
> > >
> > > *SIMPSON GUMPERTZ & HEGER** *
> > > 781.907.9000 main
> > > 781.907.9350 direct
> > > 781.907.9009 fax
> > > www.sgh.com****
> > >
> > > ****
> > >
> > > *From:* EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:
> > > EnergyPlus_Support@xxxxxxxxxxxxxxx] *On Behalf Of *Jeremiah Crossett
> > > *Sent:* Friday, February 01, 2013 1:34 PM
> > > *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > *Subject:* Re: [EnergyPlus_Support] Infiltration****
> > >
> > > ** **
> > >
> > > ****
> > >
> > > I agree with Ned, but also think it is worth mentioning that Design
> > > Builder has a simple input from blower door to Energy Plus that might be
> > > worth looking into, and I have attached a screen shot of the input. I am
> > > not 100% sure how DB applies this to its E+ file generation but assume it
> > > uses the ZoneInfiltrationDesignFlowRate Object pasted from another file
> > > below. I think there is a better way to do it with airflow network as well.
> > > ****
> > >
> > > ** **
> > >
> > > Name Infiltration****
> > >
> > > Zone or ZoneList Name Zone****
> > >
> > > Schedule Name On****
> > >
> > > Design Flow Rate Calculation Method Flow/zone****
> > >
> > > Design Flow Rate 0.018****
> > >
> > > Flow per Zone Floor Area ****
> > >
> > > Flow per Exterior Surface Area ****
> > >
> > > Air Changes per Hour ****
> > >
> > > Constant Term Coefficient 1****
> > >
> > > Temperature Term Coefficient 0****
> > >
> > > Velocity Term Coefficient 0****
> > >
> > > Velocity Squared Term Coefficient 0****
> > >
> > > ** **
> > >
> > > ** **
> > >
> > > ** **
> > >
> > > *Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions*
> > > ****
> > >
> > > *120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951***
> > >
> > > *www.phasechange.com ***
> > >
> > > ****
> > >
> > > ** **
> > >
> > > ** **
> > >
> > > ** **
> > >
> > > ** **
> > >
> > > On Fri, Feb 1, 2013 at 10:15 AM, Edward G. Lyon wrote:***
> > > *
> > >
> > > ****
> > >
> > > In my opinion, the answer to your question is very complex. I am not sure
> > > what you mean precisely by 50Pa test. Usually this means ACH50 (air
> > > changes per hour at 50 Pa), but you could have a complete test that reports
> > > Coef and Expon for the flow equation Flow = Coef*Pressure^Expon.****
> > >
> > > ****
> > >
> > > In either case there is no short cut way I see to put this data directly
> > > into EnergyPlus.****
> > >
> > > ****
> > >
> > > I also think different procedures may apply to different types of
> > > buildings. If you have a small house, and ACH50 result divided by 20
> > > (sometimes other factors) is a fair approximation of the infiltration air
> > > exchange rate for a small building. You could define Infiltration as an
> > > ACH and juggle the coefficients to give you a better guess for seasonal
> > > temperature and wind conditions. Or you could study the research on ACH50
> > > correlations to infiltration and schedule something appropriate for your
> > > location. If you have a commercial building, your test data should be unit
> > > area based and you would use Infiltration with a surface area calculation.
> > > ****
> > >
> > > ****
> > >
> > > Infiltration in EnergyPlus has a sophisticated set of input parameters
> > > intended to vary infiltration by site conditions, and I have done a lot of
> > > whole building testing. Perhaps others can provide a good reference for
> > > integrating measured data into the energy model, but I have not seen it. I
> > > think there may a way to approximate the pressure from the temperature and
> > > wind in order to recalculate coefficients for Infiltration in EnergyPlus.
> > > Perhaps I need to study this in more depth myself.****
> > >
> > > ****
> > >
> > > From my testing work I also know that not all parts of the building leak
> > > the same. There may be different results for different zones (roof to wall
> > > edges leak more than field of wall). This is likely to influence some
> > > zones more than others. Also a very leaky roof above very tight walls will
> > > give you a very leaky test result, but the actual infiltration affecting
> > > energy could be much less. ****
> > >
> > > ****
> > >
> > > For a recent model that looked at temperature conditions and not energy, I
> > > was able to use an air flow network. The equations there are more easily
> > > adaptable to the results of a building blower door test and the analysis
> > > automatically calculates pressures based on wind and temperature. This can
> > > get complicated for larger buildings, and may not work with other fans in a
> > > mechanical system.****
> > >
> > > ****
> > >
> > > Now it is not my intention to offend all the serious and dedicated energy
> > > modelers out there who put infiltration into their models. I just don�t
> > > see how it is currently much more than a guess or accepted practice, and I
> > > would be interested in any available information on correlating test data
> > > to models. I get asked that question a lot, and each energy model
> > > calculates infiltration in a slightly different way. ****
> > >
> > > ****
> > >
> > > *Ned Lyon, P.E. (MA, WV)
> > > *Staff Consultant ****
> > >
> > > *SIMPSON GUMPERTZ & HEGER** *
> > > 781.907.9000 main
> > > 781.907.9350 direct
> > > 781.907.9009 fax
> > > www.sgh.com****
> > >
> > > ****
> > >
> > > *From:* EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:
> > > EnergyPlus_Support@xxxxxxxxxxxxxxx] *On Behalf Of *FrancescoP
> > > *Sent:* Friday, February 01, 2013 12:09 PM
> > > *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > *Subject:* [EnergyPlus_Support] Infiltration****
> > >
> > > ****
> > >
> > > ****
> > >
> > > I wonder what the best ways to model infiltration in these two cases are:
> > > 1. you know the result of the blower door test (50Pa)
> > > 2. no blower door test was made but you know how the building was built
> > > Any idea?
> > > With Regards****
> > >
> > > ** **
> > >
> > > ****
> > >
> > >
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/