[EnergyPlus_Support] Re: COP of AirLoopHVAC:UnitaryHeatPump:AirToAir
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: COP of AirLoopHVAC:UnitaryHeatPump:AirToAir
- From: "FrancescoP" <direzionecontraria@xxxxxxxx>
- Date: Thu, 14 Feb 2013 14:35:47 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 14 Feb 2013 07:35:50 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1360852549; bh=8t1HapWDFx1IBh2b99N+4aAXxa/ZSEXZwikLhSw8ZY4=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=eHTVMPR9eck+4WM0Wda/lJInrtwL1S0fpQS0Nt5XqI13GSYJXV4C4lbtzmppiy2Hx4uTfPbuwIuJmtFvqyQ/Odw+F4xwYgvui99NGMdBuN1fCuAKd6Ctavm5P7h6nH6HRt5Lq8KDKZFnjXDiV/snh8+84rGPvoisr28LqMqXPOc=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=sfhJDxfaIvxeu1DzjfbdZmH/C965N2K9LNFtEsHPG7niHpUm8j8lHH02UBGKyuVDwwEK/PZ3/ukMA/9x3olRBTd0E/itJak8B0E5yKhsXE6QC2mHGeJTfn+53kSYSYe8DhCNnFPdfir47j6S/njKllQbkCAeb3eTy32zcuXDRi8=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <511B9B1D.1090500@fsec.ucf.edu>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Thank you, Mr. Raustad.
You are right: the function proposed by DesignBuilder is valid only for x values (i.e. indoor coil entering air temperature) between 12.77 and 23.88°C. I was wrong because I plotted the graph for indoor coil entering air temperature equal to 31°C. Now I have plotted the graph for indoor coil entering air temperature equal to 23°C:
http://imageshack.us/f/844/db23.jpg/
Yes, I divided heating capacity factor by EIR (energy input factor). I think that the result is the factor that multiplies the COP, isn't it? I don't understand why you wrote the "The COP is 1/EIR" (energy input factor). COP is defined as "the ratio of the rate of heat delivered to the rate of energy input".
I have plotted also come curves from RooftopPackagedHeatPump.idf
http://imageshack.us/f/716/jcip.jpg/
Yes, there are examples where both heating capacity and power increase as outdoor temps increase but capacity increases faster than power leading to an increasing COP:
http://www.rheem.co.nz/UserFiles/1/image/commercial-heat-pump-cop-vs-temp.jpg
Actually, I'm wondering whether for a baseline model for LEED certification I could use constant curves. It would be unrealistic but the baseline model has not to correspond to a real situation.
With Regards
Francesco Passerini
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad wrote:
>
> What is the range (min/max) on the x (indoor coil entering air temp) and
> y (outdoor coil entering air temp) curve inputs if used? These limits
> can influence the results (the curves output, which also has limits if
> used). Also, 31C is rather high for the indoor coil entering air temp.
> How does this look for other lower temps. You should plot at least 2
> indoor coil entering air temps on the chart to ensure the curves act
> accordingly.
>
> It looks like you divided heating capacity factor by EIR (energy input
> factor). The COP is 1/EIR which would show an increase in COP as outdoor
> temp increased.
>
> I see a downward trend in heating capacity as outdoor air temp increases
> at higher outdoor temps. Find some manufacturers data and verify this is
> correct (or look in the data sets file RooftopPackagedHeatPump.idf).
> This curve appears incorrect to me (i.e., capacity should increase as
> outdoor air temp increases). Heating capacity and power should both
> increase as outdoor temps increase. But capacity increases faster than
> power leading to an increasing EER and COP.
>
> Always question the performance curves since these are what is actually
> simulated.
>
>
> On 2/13/2013 6:35 AM, FrancescoP wrote:
> > I used curves that are used as default in DesignBuilder: DXClgCoilTotalClgCapFuncTemperature and DXClgCoilEnergyInputRatioFuncTemperature
> > They are Curve:Biquadratic
> > I have plotted them (hopefully correctly)considering the condenser temperature 31°C:
> > http://imageshack.us/f/580/dbcurves.jpg/
> > It is a "baseline model" therefore it doesn't correspond to a real HVAC system.
> > I have seen that in some examples of EnergyPlus as curves for "Total Heating Capacity Function of Temperature Curve" and for "Energy Input Ratio Function of Temperature Curve" objects Curve:Cubic are used (see AirflowNetwork_MultiZone_House.idf in that case if external temperature increases COP increases). Do you think that neglecting the influence of the condenser temperature on the COP is an acceptable approximation?
> > I simulated using those curves. Here the graph with the curves proposed by AirflowNetwork_MultiZone_House.idf :
> > http://imageshack.us/f/560/copu.jpg/
> > (comparing with the previous graph consider that in the meantime also the peak power of the heat pump was changed)
> > Probably I will develop curves using Curve:Biquadratic in order to consider both the condenser temperature and the evaporator temperature. I have found some interesting graphs in H. Ludwig von Cube et al. (1981) "Heat pump technology", Butterworths and in (1979) "Heat pump technology for saving energy", Noyes data corporation.
> >
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "FrancescoP" wrote:
> >> I am modeling System 4 - PSZ-HP according to the definition of Annex G of ASHRAE 90.1-2007. In excel I calculated the COP as ratio between "DX Coil Total Heating Rate" and "DX Heating Coil Electric Power" and I plotted the graph (outdoor air temperature ; COP) that you can see here:
> >> http://imageshack.us/f/442/copg.jpg/
> >> (when the "DX Heating Coil Electric Power" is equal to 0 I imposed the COP equal to 0)
> >> In the object AirLoopHVAC:UnitaryHeatPump:AirToAir the field "Maximum Outdoor Dry-Bulb Temperature for Supplemental Heater Operation" is equal to 4°C. I think that is the reason why the COP decreases between 3°C and 5°C: the electric heating coil switches off and the DX coil has to heat the supply air to a greater temperature.
> >> The COP decreases also when the outside temperatures are greater than 10°C. I don't understand why.
> >> Any comment, please?
> >> Best Regards
> >> Francesco Passerini
> >>
> >
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/