Re: [EnergyPlus_Support] BASELINE Centrifugal chiller partload performance curve





Richard,Jeff,
 
Thank you very much for your kindly advices.
 
Actually I used the example file(Referencebuildingforlargeofficebuilding) in which the electric chiller(autosized) COP is 5.5, But the IPLV(in the output table) is not 5.9(IPLV=5.9 is required in Standard 90.1-2007). I don't know how to adjust the coefficients to let the IPLV=5.9.
 
 
 


2013/2/15 Richard Raustad <RRaustad@xxxxxxxxxxxx>
 

Table 6.8.1C shows the minimum "rated" COP, not data for the curves. This is the value you would use for Nominal COP in the chiller objects (for this example or any other chiller type modeled).

  Chiller:Electric,
    Central Chiller,         !- Name
    AirCooled,               !- Condenser Type
    autosize,                !- Nominal Capacity {W}
    3.2,                     !- Nominal COP {W/W}

The curves are another story completely and could not be created using 90.1. To be fair, I guess you could use the same curves as the proposed building (created from manufacturers data). Or if you know that the chiller manufacturer, size, type, etc. will change, then curves for each would be required (?).

There is a chiller data set file distributed with E+ in the DataSets folder (e.g., C:\EnergyPlusV7-2-0\DataSets).



On 2/15/2013 2:19 AM, Jean Marais wrote:
You can't. With this table you can only produce a curve for COP of the chiller operating at maximum load (all be it at different water temps). Maybe James or Richard will tell me that I am wrong?

On 15 February 2013 06:58, shubou <dingwenting@xxxxxxxxx> wrote:
 

Hi,

Who can tell me how to generate the part load performance curve of centrifugal chiller according to ASHRAE STANDARD 90.1-2007 TABLE 6.8.1I?

Thank you.



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___