Hello all,
I can't understand what exactly is causing this
error:
** Severe **
AirLoopHVAC:UnitaryHeatPump:AirToAir = PSZ HP F014
HEAT PUMP
** ~~~ ** ... air flow rate =
2.9490954E-002 in fan object PSZ HP F014 SUPPLY
FAN is less than the maximum HVAC system air flow
rate in cooling mode.
** ~~~ ** The Supply Air Flow Rate During
Cooling Operation is reset to the fan flow rate
and the simulation continues.
** Severe **
AirLoopHVAC:UnitaryHeatPump:AirToAir = PSZ HP F014
HEAT PUMP
** ~~~ ** ... air flow rate =
2.9490954E-002 in fan object PSZ HP F014 SUPPLY
FAN is less than the maximum HVAC system air flow
rate in heating mode.
** ~~~ ** The Supply Air Flow Rate During
Heating Operation is reset to the fan flow rate
and the simulation continues.
The total cooling capacity is 488.18 W, so the
maximum air flow rate should be 488.18*0.00006041
= 0.029490954 m3/s
Any suggestions?
Thank you!
Miroslav
==============================
This is how the objects are defined in the .idf
file:
Branch,
PSZ HP F014 Main Branch, !- Name
0.02940954, !- Maximum Flow Rate
{m3/s}
, !- Pressure Drop
Curve Name
AirLoopHVAC:OutdoorAirSystem, !- Component 1
Object Type
PSZ HP F014 OA System, !- Component 1 Name
PSZ HP F014 Air Loop Inlet, !- Component 1
Inlet Node Name
PSZ HP F014 Mixed Air Outlet, !- Component 1
Outlet Node Name
Passive, !- Component 1 Branch
Control Type
AirLoopHVAC:UnitaryHeatPump:AirToAir, !-
Component 2 Object Type
PSZ HP F014 Heat Pump, !- Component 2 Name
PSZ HP F014 Mixed Air Outlet, !- Component 2
Inlet Node Name
PSZ HP F014 Air Loop Outlet, !- Component 2
Outlet Node Name
Active; !- Component 2 Branch
Control Type
AirLoopHVAC,
PSZ HP F014, !- Name
, !- Controller List
Name
PSZ HP F014 Availability Managers, !-
Availability Manager List Name
0.02940954, !- Design Supply Air
Flow Rate {m3/s}
PSZ HP F014 Branches, !- Branch List Name
, !- Connector List
Name
PSZ HP F014 Air Loop Inlet, !- Supply Side
Inlet Node Name
PSZ HP F014 Return Air Outlet, !- Demand Side
Outlet Node Name
PSZ HP F014 Supply Path Inlet, !- Demand Side
Inlet Node Names
PSZ HP F014 Air Loop Outlet; !- Supply Side
Outlet Node Names
Fan:OnOff,
PSZ HP F014 Supply Fan, !- Name
OFF, !- Availability
Schedule Name
0.4, !- Fan Efficiency
727, !- Pressure Rise {Pa}
0.029490954, !- Maximum Flow Rate
{m3/s}
0.825, !- Motor Efficiency
1, !- Motor In Airstream
Fraction
PSZ HP F014 Heating Coil Outlet, !- Air Inlet
Node Name
PSZ HP F014 Supply Fan Outlet; !- Air Outlet
Node Name
Coil:Cooling:DX:SingleSpeed,
PSZ HP F014 Cooling Coil,!- Name
ALWAYS_ON, !- Availability
Schedule Name
488.18, !- Rated Total Cooling
Capacity {W}
0.798655, !- Rated Sensible
Heat Ratio
3.2, !- Rated COP {W/W}
0.029490954, !- Rated Air Flow Rate
{m3/s}
, !- Rated Evaporator
Fan Power Per Volume Flow Rate {W/(m3/s)}
PSZ HP F014 Mixed Air Outlet, !- Air Inlet
Node Name
PSZ HP F014 Cooling Coil Outlet, !- Air
Outlet Node Name
PSZ HP F014 Cool Coil Cap-FT, !- Total
Cooling Capacity Function of Temperature Curve
Name
PSZ HP F014 Cool Coil Cap-FF, !- Total
Cooling Capacity Function of Flow Fraction Curve
Name
PSZ HP F014 Cool Coil EIR-FT, !- Energy Input
Ratio Function of Temperature Curve Name
PSZ HP F014 Cool Coil EIR-FF, !- Energy Input
Ratio Function of Flow Fraction Curve Name
PSZ HP F014 Cool Coil PLF, !- Part Load
Fraction Correlation Curve Name
0, !- Nominal Time for
Condensate Removal to Begin {s}
0, !- Ratio of Initial
Moisture Evaporation Rate and Steady State Latent
Capacity {dimensionless}
0, !- Maximum Cycling
Rate {cycles/hr}
0, !- Latent Capacity
Time Constant {s}
PSZ HP F014 Cooling Coil Condenser Inlet, !-
Condenser Air Inlet Node Name
AirCooled, !- Condenser Type
0, !- Evaporative
Condenser Effectiveness {dimensionless}
, !- Evaporative
Condenser Air Flow Rate {m3/s}
0, !- Evaporative
Condenser Pump Rated Power Consumption {W}
0, !- Crankcase Heater
Capacity {W}
10; !- Maximum Outdoor
Dry-Bulb Temperature for Crankcase Heater
Operation {C}
Coil:Heating:DX:SingleSpeed,
PSZ HP F014 HP Heating Coil, !- Name
ALWAYS_ON, !- Availability
Schedule Name
488.18, !- Rated Total Heating
Capacity {W}
3.2, !- Rated COP {W/W}
0.029490954, !- Rated Air Flow Rate
{m3/s}
, !- Rated Evaporator
Fan Power Per Volume Flow Rate {W/(m3/s)}
PSZ HP F014 Cooling Coil Outlet, !- Air Inlet
Node Name
PSZ HP F014 Heating Coil Outlet, !- Air
Outlet Node Name
PSZ HP F014 HP Heating Coil Cap-FT, !- Total
Heating Capacity Function of Temperature Curve
Name
PSZ HP F014 HP Heating Coil Cap-FF, !- Total
Heating Capacity Function of Flow Fraction Curve
Name
PSZ HP F014 HP Heating Coil EIR-FT, !- Energy
Input Ratio Function of Temperature Curve Name
PSZ HP F014 HP Heating Coil EIR-FF, !- Energy
Input Ratio Function of Flow Fraction Curve Name
PSZ HP F014 HP Heating Coil PLF, !- Part Load
Fraction Correlation Curve Name
PSZ HP F014 HP Heating Coil DefrEIR-FT, !-
Defrost Energy Input Ratio Function of Temperature
Curve Name
-8, !- Minimum Outdoor
Dry-Bulb Temperature for Compressor Operation {C}
, !- Outdoor Dry-Bulb
Temperature to Turn On Compressor {C}
5, !- Maximum Outdoor
Dry-Bulb Temperature for Defrost Operation {C}
0, !- Crankcase Heater
Capacity {W}
0, !- Maximum Outdoor
Dry-Bulb Temperature for Crankcase Heater
Operation {C}
ReverseCycle, !- Defrost Strategy
Timed, !- Defrost Control
0.058333, !- Defrost Time
Period Fraction
0; !- Resistive Defrost
Heater Capacity {W}
AirTerminal:SingleDuct:Uncontrolled,
F014 Air Terminal, !- Name
ALWAYS_ON, !- Availability
Schedule Name
F014 Zone Equip Inlet, !- Zone Supply Air
Node Name
0.02940954; !- Maximum Air Flow
Rate {m3/s}