Hello All,
I am working on a WSHP model. I started with the example file HeatPumpWaterToAirEquationFit.idf and have started to manipulate the file to represent a boiler/tower system with the CoolReheat dehumidification cycle. I have gotten the file to perform the way I expect without any errors. However, when I change the WSHP Supply Air Fan Operating Mode Schedule from a constant 1 to a constant 0 (which should represent unit cycling), I get the following errors:
** Severe ** CheckWarmupConvergence: Loads Initialization, Zone="SPACE1-1" did not converge after 25 warmup days.
** ~~~ ** See Warmup Convergence Information in .eio file for details.
** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL HEATING 99% DESIGN CONDITIONS DB"
** ~~~ ** ..Max Temp Comparison = 1.65 vs Temperature Convergence Tolerance=0.40 - Fail Convergence
** ~~~ ** ..Min Temp Comparison = 1.08E-003 vs Temperature Convergence Tolerance=0.40 - Pass Convergence
** ~~~ ** ..Max Heat Load Comparison = 1.0068 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** Severe ** CheckWarmupConvergence: Loads Initialization, Zone="SPACE2-1" did not converge after 25 warmup days.
** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL HEATING 99% DESIGN CONDITIONS DB"
** ~~~ ** ..Max Temp Comparison = 1.05 vs Temperature Convergence Tolerance=0.40 - Fail Convergence
** ~~~ ** ..Min Temp Comparison = 1.94E-004 vs Temperature Convergence Tolerance=0.40 - Pass Convergence
** ~~~ ** ..Max Heat Load Comparison = 2.4403 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** ~~~ ** ..Max Cool Load Comparison = 0.4412 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** Severe ** CheckWarmupConvergence: Loads Initialization, Zone="SPACE3-1" did not converge after 25 warmup days.
** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL HEATING 99% DESIGN CONDITIONS DB"
** ~~~ ** ..Max Temp Comparison = 3.54 vs Temperature Convergence Tolerance=0.40 - Fail Convergence
** ~~~ ** ..Min Temp Comparison = 7.09E-004 vs Temperature Convergence Tolerance=0.40 - Pass Convergence
** ~~~ ** ..Max Heat Load Comparison = 6.1600E-002 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads Convergence Tolerance=4.00E-002 - Fail Convergence
** Severe ** CheckWarmupConvergence: Loads Initialization, Zone="SPACE4-1" did not converge after 25 warmup days.
** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL HEATING 99% DESIGN CONDITIONS DB"
** ~~~ ** ..Max Temp Comparison = 2.54 vs Temperature Convergence Tolerance=0.40 - Fail Convergence
I tried autosizing the plant as well and am getting the same result/problem.
So I guess the final question is this a big deal? And if it is, how might I go about fixing it?
Thanks for the help!
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___
- Follow-Ups:
- [EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- From: Jean marais
- Prev by Date: [EnergyPlus_Support] N++ - new GUI for EnergyPlus released for beta testing
- Next by Date: [EnergyPlus_Support] High cooling load simulation (data center)
- Previous by thread: [EnergyPlus_Support] N++ - new GUI for EnergyPlus released for beta testing
- Next by thread: [EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- Index(es):