[EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- From: "Jean marais" <jeannieboef@xxxxxxxxx>
- Date: Tue, 12 Mar 2013 06:51:03 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 12 Mar 2013 00:51:07 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1363071066; bh=DkDMiPx7QBdK+UrW2XSsTuwf96QUxwr/tpdJ9BIISYs=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=x92rwhRQarC71u8vBpayrE+hE+EqmMXEQblB6NC7L+UoIvpx+/Eg8ObbRf0B3sx0kRasajmTyCSa8BVo/d6V3fL2EbZPVG9b6F9zoKGfwZZwPONksKIRIIWFBx9iYeTXrTwWs3xZcJGBfdJO5UcyIstyKLBWYJ0ywvLZnvNGjR8=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=e9S3qFOhmkaU1wYayvgzNl/GDkXHF2PdBD2qVDGfdBF6w8s3ytmKhQgCmfONii+WFvYvCxUw3fWBM5w3wt909rff7LaoWz7ksK6JqC1yzybCxh8YIsF2AhM8cSDS7veBS6l4WZRBG4hgSz7/MzASmrnTBIVFR+TbtLpldqL5XFM=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <khlb0h+pbdn@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
The rule of thumb is that as long as you can't explain the error, it remains a problem. Are you "switching off" all the associated componants like fans as well?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "tr1g92" <trig92@...> wrote:
>
>
> Hello All,
>
> I am working on a WSHP model. I started with the example file
> HeatPumpWaterToAirEquationFit.idf and have started to manipulate the
> file to represent a boiler/tower system with the CoolReheat
> dehumidification cycle. I have gotten the file to perform the way I
> expect without any errors. However, when I change the WSHP Supply Air
> Fan Operating Mode Schedule from a constant 1 to a constant 0 (which
> should represent unit cycling), I get the following errors:
>
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE1-1" did not converge after 25 warmup days.
> ** ~~~ ** See Warmup Convergence Information in .eio file for
> details.
> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
> HEATING 99% DESIGN CONDITIONS DB"
> ** ~~~ ** ..Max Temp Comparison = 1.65 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 1.08E-003 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 1.0068 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE2-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
> HEATING 99% DESIGN CONDITIONS DB"
> ** ~~~ ** ..Max Temp Comparison = 1.05 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 1.94E-004 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 2.4403 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 0.4412 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE3-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
> HEATING 99% DESIGN CONDITIONS DB"
> ** ~~~ ** ..Max Temp Comparison = 3.54 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 7.09E-004 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 6.1600E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE4-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
> HEATING 99% DESIGN CONDITIONS DB"
> ** ~~~ ** ..Max Temp Comparison = 2.54 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 6.77E-004 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 3.9986E-003 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 0.6022 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE5-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
> HEATING 99% DESIGN CONDITIONS DB"
> ** ~~~ ** ..Max Temp Comparison = 9.19E-004 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Min Temp Comparison = 0.32 vs Temperature Convergence
> Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 1.0964E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 0.1821 vs Loads
> Convergence Tolerance=4.00E-002 - Fail Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE1-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
> WMO#=725300"
> ** ~~~ ** ..Max Temp Comparison = 0.63 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 4.68E-002 vs Temperature
> Convergence Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 1.8529E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 2.4692E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE2-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
> WMO#=725300"
> ** ~~~ ** ..Max Temp Comparison = 0.89 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 0.19 vs Temperature Convergence
> Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 1.5899E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 1.5204E-003 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** Severe ** CheckWarmupConvergence: Loads Initialization,
> Zone="SPACE4-1" did not converge after 25 warmup days.
> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
> WMO#=725300"
> ** ~~~ ** ..Max Temp Comparison = 6.94 vs Temperature Convergence
> Tolerance=0.40 - Fail Convergence
> ** ~~~ ** ..Min Temp Comparison = 0.13 vs Temperature Convergence
> Tolerance=0.40 - Pass Convergence
> ** ~~~ ** ..Max Heat Load Comparison = 2.2936E-002 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** ~~~ ** ..Max Cool Load Comparison = 2.9675E-003 vs Loads
> Convergence Tolerance=4.00E-002 - Pass Convergence
> ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
> loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 10/09 19:15 - 19:30
> ** ~~~ ** The solution for one or more of the Air Loop HVAC
> systems did not appear to converge
> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 4 did not
> converge for mass flow rate
> ** ~~~ ** Check values should be zero. Most Recent values listed
> first.
> ** ~~~ ** Demand-to-Supply interface mass flow rate check value
> iteration history trace:
> 0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,\
> 0.329702,0.329702,
> ** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check
> value iteration history trace:
> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
> 0.000000,0.000000,
> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 4 did not
> converge for energy
> ** ~~~ ** Check values should be zero. Most Recent values listed
> first.
> ** ~~~ ** Demand-to-Supply interface energy check value iteration
> history trace:
> 7110.109302,7110.109302,7110.109302,7110.109302,7110.109302,7110.109302,\
> 7110.109302,7110.109302,7110.109302,7110.109302,
> ** ~~~ ** Supply-to-demand interface deck 1 energy check value
> iteration history trace:
> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
> 0.000000,0.000000,
> ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
> loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 12/21 19:45 - 19:50
> ** ~~~ ** The solution for one or more of the Air Loop HVAC
> systems did not appear to converge
> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 1 did not
> converge for mass flow rate
> ** ~~~ ** Check values should be zero. Most Recent values listed
> first.
> ** ~~~ ** Demand-to-Supply interface mass flow rate check value
> iteration history trace:
> 0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,\
> 0.427247,0.427247,
> ** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check
> value iteration history trace:
> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
> 0.000000,0.000000,
> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 1 did not
> converge for energy
> ** ~~~ ** Check values should be zero. Most Recent values listed
> first.
> ** ~~~ ** Demand-to-Supply interface energy check value iteration
> history trace:
> 9453.547566,9453.547566,9453.547566,9453.547566,9453.547566,9453.547566,\
> 9453.547566,9453.547566,9453.547566,9453.547566,
> ** ~~~ ** Supply-to-demand interface deck 1 energy check value
> iteration history trace:
> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
> 0.000000,0.000000,
>
> I tried autosizing the plant as well and am getting the same
> result/problem.
>
> So I guess the final question is this a big deal? And if it is, how
> might I go about fixing it?
>
> Thanks for the help!
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/