Re: [EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: Re: [EnergyPlus_Support] Re: HeatPumpWaterToAirEquationFit Problem
- From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
- Date: Tue, 12 Mar 2013 07:43:32 -0400
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 12 Mar 2013 05:43:36 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1363088615; bh=QxQ5+mjkrelnBfkb41CMTkavDjc5PtbAlRWDV4jl9wc=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:In-reply-to:To:Message-id:Organization:User-Agent:References:X-Originating-IP:X-eGroups-Msg-Info:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=mV2ykEnOMf+BALxsDTJtXtFqRlOZBYFe65Pgk9Q+2/Kvzl8JhT0a6iyLXV2YU7CxcaDtWiJAM5+p8uaoIkGaBByrNnWQP2xRBuiTR14WwlixUl9J79M9ppUScsPedjEe8UBK55U3m0vUsaD780t1cb46IXS9Jt1PDigBcyoD0hE=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=Ga7dYlcjmz2UBgUVcDIgtFtSLDeyHhfQsRaYbcpeonCtQa7wWgpcYPbYyFUNRWATF10LaZVYbm7Y35Wpy/detmiVNQolzZuVVpdF3vhV6gfZfiJj6DIbPqiItU8+DPzJn65Urj5LPLdelP5eoYMstCdlROFluZJbNB48yntHk4g=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <khmj8n+8na0@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Organization: Florida Solar Energy Center
- References: <khmj8n+8na0@eGroups.com>
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: Mozilla/5.0 (Windows NT 5.1; rv:17.0) Gecko/20130215 Thunderbird/17.0.3
How does the example file respond when changing the Fan Operating Mode
Schedule?
On 3/12/2013 2:51 AM, Jean marais wrote:
> The rule of thumb is that as long as you can't explain the error, it remains a problem. Are you "switching off" all the associated componants like fans as well?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "tr1g92" <trig92@...> wrote:
>>
>> Hello All,
>>
>> I am working on a WSHP model. I started with the example file
>> HeatPumpWaterToAirEquationFit.idf and have started to manipulate the
>> file to represent a boiler/tower system with the CoolReheat
>> dehumidification cycle. I have gotten the file to perform the way I
>> expect without any errors. However, when I change the WSHP Supply Air
>> Fan Operating Mode Schedule from a constant 1 to a constant 0 (which
>> should represent unit cycling), I get the following errors:
>>
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE1-1" did not converge after 25 warmup days.
>> ** ~~~ ** See Warmup Convergence Information in .eio file for
>> details.
>> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
>> HEATING 99% DESIGN CONDITIONS DB"
>> ** ~~~ ** ..Max Temp Comparison = 1.65 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 1.08E-003 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 1.0068 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE2-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
>> HEATING 99% DESIGN CONDITIONS DB"
>> ** ~~~ ** ..Max Temp Comparison = 1.05 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 1.94E-004 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 2.4403 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 0.4412 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE3-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
>> HEATING 99% DESIGN CONDITIONS DB"
>> ** ~~~ ** ..Max Temp Comparison = 3.54 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 7.09E-004 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 6.1600E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 1.0000 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE4-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
>> HEATING 99% DESIGN CONDITIONS DB"
>> ** ~~~ ** ..Max Temp Comparison = 2.54 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 6.77E-004 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 3.9986E-003 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 0.6022 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE5-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(SizingPeriod)="CHICAGO_IL_USA ANNUAL
>> HEATING 99% DESIGN CONDITIONS DB"
>> ** ~~~ ** ..Max Temp Comparison = 9.19E-004 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Min Temp Comparison = 0.32 vs Temperature Convergence
>> Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 1.0964E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 0.1821 vs Loads
>> Convergence Tolerance=4.00E-002 - Fail Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE1-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
>> WMO#=725300"
>> ** ~~~ ** ..Max Temp Comparison = 0.63 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 4.68E-002 vs Temperature
>> Convergence Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 1.8529E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 2.4692E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE2-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
>> WMO#=725300"
>> ** ~~~ ** ..Max Temp Comparison = 0.89 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 0.19 vs Temperature Convergence
>> Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 1.5899E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 1.5204E-003 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** Severe ** CheckWarmupConvergence: Loads Initialization,
>> Zone="SPACE4-1" did not converge after 25 warmup days.
>> ** ~~~ ** ...Environment(RunPeriod)="CHICAGO IL USA TMY2-94846
>> WMO#=725300"
>> ** ~~~ ** ..Max Temp Comparison = 6.94 vs Temperature Convergence
>> Tolerance=0.40 - Fail Convergence
>> ** ~~~ ** ..Min Temp Comparison = 0.13 vs Temperature Convergence
>> Tolerance=0.40 - Pass Convergence
>> ** ~~~ ** ..Max Heat Load Comparison = 2.2936E-002 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** ~~~ ** ..Max Cool Load Comparison = 2.9675E-003 vs Loads
>> Convergence Tolerance=4.00E-002 - Pass Convergence
>> ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
>> loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 10/09 19:15 - 19:30
>> ** ~~~ ** The solution for one or more of the Air Loop HVAC
>> systems did not appear to converge
>> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 4 did not
>> converge for mass flow rate
>> ** ~~~ ** Check values should be zero. Most Recent values listed
>> first.
>> ** ~~~ ** Demand-to-Supply interface mass flow rate check value
>> iteration history trace:
>> 0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,0.329702,\
>> 0.329702,0.329702,
>> ** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check
>> value iteration history trace:
>> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
>> 0.000000,0.000000,
>> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 4 did not
>> converge for energy
>> ** ~~~ ** Check values should be zero. Most Recent values listed
>> first.
>> ** ~~~ ** Demand-to-Supply interface energy check value iteration
>> history trace:
>> 7110.109302,7110.109302,7110.109302,7110.109302,7110.109302,7110.109302,\
>> 7110.109302,7110.109302,7110.109302,7110.109302,
>> ** ~~~ ** Supply-to-demand interface deck 1 energy check value
>> iteration history trace:
>> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
>> 0.000000,0.000000,
>> ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
>> loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 12/21 19:45 - 19:50
>> ** ~~~ ** The solution for one or more of the Air Loop HVAC
>> systems did not appear to converge
>> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 1 did not
>> converge for mass flow rate
>> ** ~~~ ** Check values should be zero. Most Recent values listed
>> first.
>> ** ~~~ ** Demand-to-Supply interface mass flow rate check value
>> iteration history trace:
>> 0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,0.427247,\
>> 0.427247,0.427247,
>> ** ~~~ ** Supply-to-demand interface deck 1 mass flow rate check
>> value iteration history trace:
>> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
>> 0.000000,0.000000,
>> ** ~~~ ** Air System Named = WAHP PACKAGE SINGLE ZONE 1 did not
>> converge for energy
>> ** ~~~ ** Check values should be zero. Most Recent values listed
>> first.
>> ** ~~~ ** Demand-to-Supply interface energy check value iteration
>> history trace:
>> 9453.547566,9453.547566,9453.547566,9453.547566,9453.547566,9453.547566,\
>> 9453.547566,9453.547566,9453.547566,9453.547566,
>> ** ~~~ ** Supply-to-demand interface deck 1 energy check value
>> iteration history trace:
>> 0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,0.000000,\
>> 0.000000,0.000000,
>>
>> I tried autosizing the plant as well and am getting the same
>> result/problem.
>>
>> So I guess the final question is this a big deal? And if it is, how
>> might I go about fixing it?
>>
>> Thanks for the help!
>>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/