[EnergyPlus_Support] Re: High cooling load simulation (data center)
The warnings are related to one another...the main problem here is your chilled water is at 120 deg C in the plant loop. This is obviously wrong. You need to find out why. What is transfering heat to this fluid...the end-users on the demand side, pumps operating at insane conditions with a badly matching pump curve, anything else?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Diego Lima <diegocambuca@...> wrote:
>
> Hi all,
> I�m working on a data center simulation and due to the high colling load (1MW) on a small area (560m�) I have a lot of warnings. The simulation is running, but I�m trying to reduce the number of wanings.
>
> The main warnigs are:
> � �************ �** Warning ** Plant loop exceeding upper temperature limit, PlantLoop="CHILLED WATER LOOP"
> � �************* �** � ~~~ � ** � This error occurred 537739 total times;
> � �************* �** � ~~~ � ** � during Warmup 7255 times;
> � �************* �** � ~~~ � ** � during Sizing 0 times.
> � �************* �** � ~~~ � ** � Max=140.281491
> � �*************
> � �************* �** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> � �************* �** � ~~~ � ** � This error occurred 4978717 total times;
> � �************* �** � ~~~ � ** � during Warmup 0 times;
> � �************* �** � ~~~ � ** � during Sizing 0 times.
> � �************* �** � ~~~ � ** � Max=462.436949 C �Min=442.956365 C
> � �*************
> � �************* �** Warning ** GetSpecificHeatGlycol: Temperature out of range (too high) for fluid specific heat
> � �************* �** � ~~~ � ** � This error occurred 32126400 total times;
> � �************* �** � ~~~ � ** � during Warmup 0 times;
> � �************* �** � ~~~ � ** � during Sizing 0 times.
> � �************* �** � ~~~ � ** � Max=380.57589 {C} �Min=125. {C}
> � �*************
> � �************* �** Warning ** GetDensityGlycol: Temperature out of range (too high) for fluid density
> � �************* �** � ~~~ � ** � This error occurred 6452375 total times;
> � �************* �** � ~~~ � ** � during Warmup 0 times;
> � �************* �** � ~~~ � ** � during Sizing 0 times.
>
> I appreciate if you help me with some tips.
>
> Thanks,
>
> Diego.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/