The true definition would be per surface and is as described in e+ documentation. However, ASHRAE 90.1 dictates the factor should be read of a table (regardless of perimeter) and is thereby assuming a 150mm slab with xmm insulation...I.e. becomes a factor of insulation only. So you work backwards: get the required F-factor from table 5.x, lookup the corresponding F-Factor in Appendix A to find the required insulation R-value for your 150mm slab. Create a 150mm construction with a insulation as found, and wolla, you have the baseline required slab. For more info check appx A. Jean Marais Sent from my iPhone
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.