Jean,
My only comment is that I've always modeled the slab as carpeted.
Therefore, the foundation layer always starts with a carpet (or what
a colleague used to call "RUGNPAD" :-) ) that's modeled as a pure
resistance layer of R-1.08 (in IP). This doesn't affect the total
R-value of the modeled slab, just reduces the R-value of the
fictitious soil layer, but it does have an important effect in
decoupling somewhat the thermal mass of the concrete from the room
heat balance, which is the effect of the carpet.
For anyone interested, I've just scanned the old 1988 ASHRAE paper
("Whole-House Simulation of Foundation Heat Flows Using the DOE-2.1C
Program", by Huang, Y.J., L. Shen, J. Bull, and L. Goldberg) and
put it on the Web
(www.whiteboxtechnologies.com/PAPERS/88_YJH_etal_Fdn_Model.pdf)
because it was the technical basis for the Winklemann article.
Please notice that the analysis, which was done for the Building
Foundation Design Handbook ( Labs et al., Univ. of Minn Underground
Space Center, 1988 now out of print), directly imported the heat
flows from the 2-D foundation model into the DOE-2.1C simulations,
similar to using the Slab program with EnergyPlus. The U-effectives
(or F Factors) were calculated for two purposes: (1) to adjust the
foundation heat flows for the actual space temperature, and (2) to
give readers a rough idea of the net difference in heat flows
between the 88 foundation measures. I never thought of them as a
stand-alone calculation method, so it's been quite surprising to
find them still referenced 25 years later. Warning: the PDF is
quite large (over 26MB) because it was all scanned.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/29/2013 3:36 AM, Jean Marais wrote:
My goal is to reverse engineer an
equivalent slab-on-grade construction for
simulations as per ASHRAE 90.1 Appx G.
F * Pexp = Ueff * A
= 1/Reff * A
This gives
Reff = A / (F * Pexp)...the user inputs
...therefor for a insulation rating value
that matches the standard's rated insulation
requirement for the required F-factor and
substituting for the construction build up as
defined by ASHRAE 90.1 A6
Reff = Rairfilm_in + Rconcreate +
Rrequired_rated_insulation + Rsoil + Rother +
Rairfilm_out
where
*********************************
Rairfilm_in = 0.77 hr-ft2-F/Btu (0.14 m2-K/W)
is the average of the air film resistance for heat
flow up 0.61 hr-ft2-F/Btu (0.11 m2-K/W) and heat
flow down 0.92 hr-ft2-F/Btu (0.16 m2-K/W), as per
ASHRAE 90.1 A9.1.4 and Winkelmann
*************************************
Rconcreate = 0.07 m²K /W
as per ASHRAE 90.1 A6 for 0.5ft (150 mm)
concrete from ASHRAE 90.1 Table A3.1B, and density
2304 kg/m³
**********************************
Rrequired_rated_insulation can be found by fitting
a curve through the values in standard 90.1 Table A6.3
for fully insulated slab-on-grade:
| ASHRAE 90.1 F-Factors for fully
insulated slabs and Unheated as per Appendix G |
|
|
|
|
|
|
|
|
| SI Units |
|
|
|
|
|
|
|
|
|
|
|
|
|
| R-values |
0 |
0.9 |
1.3 |
1.8 |
2.6 |
3.5 |
4.4 |
5.3 |
6.2 |
7 |
7.9 |
8.8 |
9.7 |
| F-factors |
na |
0.8 |
0.71 |
0.62 |
0.52 |
0.45 |
0.4 |
0.37 |
0.34 |
0.32 |
0.3 |
0.29 |
0.28 |
we can find the curve fit equation as
Rrequired_rated_insulation = 0.6065 * (
F )-2.165
****************************************
Rsoil is assumed 1 ft (0.3 m) at k=1.3 W/m²-K as per
Table A9.4D, which corrisponds to recommendations in
UNDERGROUND SURFACES: HOW TO GET A BETTER UNDERGROUND
SURFACE HEAT TRANSFER CALCULATION IN DOE-2.1E,
Winkelmann
therefore
Rsoil = 0.22 m²K /W
**************************************
Rairfilm_out = 0.0299387 m²K /W as per ASHRAE 90.1
A9.4.1
*************************************
Therefore the only unknown, Rother can be calculated.
Rother = A / (F * Pexp) - (0.14) - (0.07)
- (0.6065 * ( F )-2.165)
- (0.22) - (0.0299387)
it is assumed Rother has material properties for
density and specific heat, the same as that of soil.
xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
Now I can build up an equivalent construction for the
"slab" espectially honed to exclusively "slab-on-grade"
for Appendix G of ASHRAE 90.1. If Rother is negative,
Rrequired_rated_insulation must be "derated" to effect
the difference. See the spreadsheet attatched.
Thanks for all the help.
Jean.
PS other material properties one can use to build up
this construction in e+ could be as follows
| Concrete |
150 mm |
Construction as per A6.1: |
|
|
|
|
|
Properties as per A3.1B for 150
mm, 2304 kg/m³ --> Rc = 0.07, HC = 294 --> |
|
|
specific heat = |
850.694444 |
J/kg-K |
|
|
|
|
| Insulation R- |
|
0.36521482 |
m²K/W |
|
|
|
|
|
Properties as per HOF Expanded
Polystyrene extruded smooth skin 40 kg/m³, 0.030
W/m²-K |
|
thickness = |
0.01095644 |
mm |
|
|
|
|
| Soil |
to account for thermal mass
effects of the soil as per DOE-2 Articles from
the Building Energy Simulation User News,
January 2003 and ASHRAE 90.1 table A9.4D |
|
|
|
k = |
1.3 |
W/m²-K |
|
|
|
|
|
thickness = |
0.3 |
m |
|
|
|
|
|
density = |
1840 |
kg/m³ |
as per DOE-2 referenced above |
|
On 29 April 2013 10:19, Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx>
wrote:
Jean,
My comments follow your questions below.
On 4/29/2013 12:05 AM, Jean Marais wrote:
Hi Joe,
I'm not getting any
further on this issue.
Perhaps you can lend me
some insight. You say
that the F-factors in
standard 90.1 were the
result of parametric
simulations that you ran
for different
configurations of
perimeter
insulation...so let me
see if I understand this
right.
1) your model (1988)
assumed the walls were
Adiabatic so that only the
heat loss through the
slab-on-grade was captured
No, the 2-D simulations I did were with a
finite-difference program for a vertical 1 ft.
slice through the foundation extending 15 ft into
the building.
In the original analysis done for the Foundation
Design Handbook in 1988, I multiplied the heat
flow of each FD element by the annulus length of a
1540-ft2 house (55 ft x 28 ft) to derive the total
heat flow through the foundation. For the simpler
method described in Winklemann and Huang,
I took the total heat flows across the entire 15
ft foundation slice and divided that by
temperature difference (Tin - Tout) to derive the
F-Factors per lineal foot of perimeter. This
actually overestimates the heat flows due to the
core section, but is a lot easier to calculate.
So, I repeat - no heat losses
are being ignored, just that their magnitude is
assumed to be a function of the perimeter length.
2) you considered
vertical, horizontal AND
fully insulated
configurations
I did 88 foundation configurations for slab on
grade, 8' full basements, 4' half basements, and
ventilated crawl spaces. Slab configurations
include two depths of vertical perimeter edge
insulation (2' and 4') either R-5, R-10, or R-15,
on the outside or inside of the slab, and also
combinations of vertical and horizontal extending
down 2' and out 2' (this turned out to be the most
effective, as it decoupled more of the soil from
the outside air temperatures). Basement insulation
is similar, 4' 8' insulation outside, inside, and
integral (for a wood frame foundation), crawl
space configurations are similar to the slab
configurations. I think all 88 cases are
described in both the 88 ASHRAE paper as well as
the Winkelmann Huang paper.
3) you used a 2D slab
simulation program
Yes, it was a 2-D finite difference program
written by Lester Shen at the Univ. of Minnesota
Underground Space Center. We did 5 years of
initialization, 4 on a monthly time step, 1 on a
daily time step, followed then by one year on a
daily timestep. The program was very robust, no
problems at all.
4) what inside air film resistance
did you use?
You have to distinguish the air film resistances
used in the 2-D simulations, and the ones used in
the whole building simulation incorporating the
2-D results. I think we used pretty standard
ASHRAE values for the air film, maybe 0.77
Btu/hr-ft2-F . This actually gets rather academic
because the total effective R-value of the
foundation including the soil is quite high, R-20
to R-40, especially when "coupled" with the
outside air temperature.
5) what outside air film
resistance did you use?
I believe it was a constant 0.17 Btu/hr-ft2-F in
the 2-D simulation, but in the whole house
simulation, this varied depending on wind speed.
Not a big effect.
6) what inside temperature did you
use?
Same caveat applies here. In the 2-D simulation,
Tin was constant 74F for the slab, lower for the
basement and crawl space, either 60 F or 65F. In
the DOE-2 simulation, the zone temperature varies
quite a bit, for which DOE-2 does a UA delta T
correction using the same F-Factor. This
adjustment was
especially large for the basement and crawl space,
and Lester and I came up with a crude response
factor to take into account the thermal lag due to
the large amount of thermal mass. That was
written up in the 1988 paper, but I did not
emphasize it in the simpler models.
7) what outside temperature did you
use? If it varied over time, how is it
that the F-factor can be constant? If it
varied by Climate Zone, R-value, or
other, could you tell me the breakdown?
The outside temperature is the daily outdoor air
temperature. There's also a constant deep ground
temperature 50 ' down in the model. Think of the
F-Factor as a conductance, so it scales with the
temperature difference (Tin - Tout). It's the
crudest first-order approximation because it
doesn't take
the thermal lag of the soil into account, nor does
it distinguish between the temperatures of the
air, ground, and deep ground. What I did were
linear
regressions of the heat flux through the
foundation against the instantaneous temperature
difference Tin - Tout, averaged for 12 different
climates.
That was why when I did the project for the Energy
Commission a decade later, I split the foundation
into different domains and did separate
regressions for 3-week air temperature, 5' ground
temperature, and deep ground constant temperature.
On 25 April 2013 12:09, Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx>
wrote:
Jean, others,
It was quite a surprise to read your
e-mail and find that the old
F-Factors that I calculated back in
1988 are still being referred to in
Standard 90.1. If you're interested
in more details of that effort,
there's an ASHRAE Transaction paper
Huang, Y.J., L.S. Shen,
J.C. Bull, and L.F. Goldberg
1988. "Whole-house simulation of
foundation heat-flows using the
DOE-2 program",
ASHRAE Transactions, Vol.
94-2.
and a 1998 User News
article written by Fred
Winkelmann on its implementation
in DOE-2 (see attached).
The F-Factors are per
lineal feet of perimeter from
Tout to Tin of the space
containing the foundation. There
are actually several ways to
implement this model: (1) model
a monolithic foundation as an
exterior wall and adjust the
R-value of the layer so that
U*A = F*PL (Perimeter length) --
this is the method shown in the
Winkelmann article, (2)
decompose the foundation into
two regions - a perimeter strip
1-2 ft wide and a core for the
remainder; model the perimeter
as an exterior wall, adjusting
its R-value accordingly, but
model the core as an adiabatic
layer. When I was working with
DOE-2, there was a practical
problem that layers can't be too
thick or the response factor
would fail, so I could only add
at most 2.5 ft of soil. I don't
know if EnergyPlus has similar
limitations. Ideally, you would
want to model as much soil as
possible to get the thermal
dampening effect.
The main deficiencies with
this technique are (1) Tout is
the outside air temperature, (2)
the foundation is treated as a
single layer. I know there's a
temptation to model the
foundation as a underground
layer tied to the soil
temperature, but that would be
wrrong since the F-Factors are
calculated air-to-air.
In the late 90's
(1998-2000), I worked with Fred
Winkelmann and Vladimir Bazjanac
for the Calif. Energy Commission
to develop what I think is a
much better model that is now
the approved method for
Title-24. This model uses a
similar approach as before,
except instead of a single
F-Factor, there are six
Foundation Conductances for two
domains (perimeter and core) and
three heat flow paths ("quick"
to the outdoor air temperature
the past 3 weeks, "slow" to the
monthly ground temperature, and
"constant" to the deep ground
temperature). The model is not
only more accurate, but more
flexible for different building
conditions. If anyone's
interested in the report, it's
available at www.whiteboxtechnologies.com/downloads/00_02.YJH.CEC_Fdn_Model.pdf
If I have it in my power,
I would urge everyone to stop
using the 1988 model and switch
to the 2000 model, but since the
F-Factors seem to have been
institutionalized by now, that
would be irresponsible. So, I'll
be happy to answer questions
about the use of either model.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/24/2013 9:34 PM, Jean
marais wrote:
Dear Group,
e+ has a documented
technique of
converting the user
inputs of F-Factor,
Area and Perimeter
into a Equivalent
U-Value Contruction.
It seams however that
ASHRAE 90.1 and HOF
has too little
information on how the
F-Factors in standard
90.1 were created (for
example, which T_in
and T_out were used,
how were losses into
the soil accounted
for, which air film
resistances were used,
etc.) for me to trust
this technique as a
compliance tool.
I propose the
following solution:
Baseline case...
In a nut shell, a
curve fit for the
"fully insulated" case
of the F-factor table
in 90.1...R-insulation
is then a function of
F-factor input. Thus
an equivalent
construction can be
created that satisfies
the Standard in terms
of Rated R-insulation
covering the entire
slab, concrete
thickness and soil
conductivity as per
the description in
Appx A. As Dr Huang
suggested, use a 0.3
(also noted for this
thickness at the back
of 90.1 appx A) at the
soil conductivity
perscribed by 90.1 to
catch the thermal mass
effects of the soil.
As a check, a
construction defined
in this way can be
looked up for its
F-factor and should
give the right R-value
using interpolation.
Proposed case...
1) look at the actual
design
2) deturmin the
F-factor from Table
A6.3
3) Calculate
equivalent slab
construction as for
Baseline case using
the F-factor from step
2)
It should be said that
if your slab does not
meet the criteria for
"slab-on-grade" as per
90.1, then the
standard has no
requirement of it and
it should be modelled
identically to that of
the proposed case
model (e.g. Basement
slabs are not
slab-on-grade)
Your comments please,
after reading some of
the rest of these
corrispondances.
Kind regards,
Jean
Further reading...
I would like to draw
your attention to how
COMcheck software
handles slab-on-grade
F-factors.
http://www.energycodes.gov/sites/default/files/documents/BECP_Technical%20Support%20Document%20for%20Version%20391%20of%20the%20COMcheck%20Software_Sept2012_v00.pdf
Another interesting
take is that of DOE2 http://simulationresearch.lbl.gov/dirpubs/un_articles02.pdf
The tabled F-factors
here were deturmined
by Huang using 2D
parametric
studies...the
tabulated values don't
match those in ASHRAE
90.1. See the
onebuilding forum note
by Joe Huang http://www.gard.com/ml/bldg-sim-archive/msg01047.html
Comments, please.
Kind regards,
Jean Marais
On 19 April 2013
16:59, Tianzhen Hong
<thong@xxxxxxx> wrote:
Jean,
When we developed this
feature for
EnergyPlus, we did
quite some research on
the topic and you also
pointed out, ASHRAE
did not have every
details on F-factor. A
few years back, I was
developing EnvStd, a
tool used for ASHRAE
90.1 envelope
tradeoff, F-factor was
used to calculate the
equivalent heat
transfer between the
zone and outdoor,
there is no such a
term of "heat flow
into soil
environment".
Tianzhen
On Fri, Apr 19, 2013
at 2:32 AM, Jean
Marais <jeannieboef@xxxxxxxxx>
wrote:
HOF 18.31 equation 41
with equation 42 for
"at grade surfaces"
can be combined as
follows:
q = Pexp*F*delta_t
...unfortuanately
delta_t is not defined
here...judging from
the previous section
for slabs below grade,
I must currently
assume delta_t = (T_in
- T_ground), though
for perimeter losses
delta_t = (T_in -
T_ODA) may be more
appropriate.
In context of slabs
below grade, I see
that the for heat to
travel from T_in to
T_ground, it must
travers Rfilm_in,
Rcon, Rinsulation (if
any) and possibly a
R_soil_to_slab
(probably negligable).
However, for slabs at
grade the heat travels
partly into the ground
and partly into the
ODA via the ground.
i.e. I could assume
that the F-factors
were calculated
somewhat as below:
qtot = heat flow into
soil environment +
heat flow into outdoor
environment through
perimeter effects
= [Area *
U_slabconstructionwithinteriorairfilmresistances
* (T_in - T_ground)] +
[Pexp * F * (T_in -
T_ODA)]
= [Area /
(Rfilm_in+Rcon+Rins) *
(T_in - T_ground)] +
[Pexp /
(Rfilm_in+Rcon+Rins+Rsoil_path_to_outdoors+Rvertical_insulation+Rfilm_out)
* (T_in - T_ODA)]
...there is a small
overlap here, but
should be negligable.
As you can see, if
this is the case,it is
very important to
establish what
Rsoil_path_to_outdoors
was used for the
F-factor ratings in
90.1. Alternatively,
1) soil conductivity
used for the F-factor
ratings in 90.1 = 1.30
W/m-K as per A6.1
2) soil heat flow path
length for the
F-factor ratings in
90.1...can be assumed
the distance of the
corrisponding F-factor
insulation and type.
E.g. F-0.90
corrisponds to R-1.8
and 600 mm vertical
insulation, which
approximates a soil
travel path of 2x600
mm.
HOF does not mention
any air film
resistances in chapter
18.31, but 90.1 lists
these for rating
values in A9.4.1.
Assuming an average
for heat flow up and
down is probably a
good approximation for
the interior air film
resistances as the
temperature of the
soil cycles over the
annual average for
half the year and
under the average for
the other half
(sinusoidal).
The values in HOF
table 24 are in the
same range as those in
90.1 table A6.3.
Furthermore, HOF
equation 42 defines q
= heat loss through
perimeter...this leads
me to believe that the
F-factor rating values
in 90.1 express only
heat losses of
perimeter effects and
does not include those
to the soil.
In summary:
INPUT VALUES
F-factor
Pexp
Area
T_ground =
anual_mean_ground_temperature
used for the F-factor
rating values is
assumed at 0.3 m...0.3
from Winkelmann's
slab-on-grade
model...we assume the
rating values of 90.1
included variation per
climate zone and that
this corrisponds to
user input.
T_in =
anual_mean_indoor_temperature
used for the F-factor
rating values is
assumed to have been
assumed at 20ºC for
conditioned spaces
T_ODA =
annual_mean_outdoor_temperature
...it is assumed that
the F-factor rating
values had assumed the
annual_mean_outdoor_temperature
for calculation and
that climate zone
variation was taken
into account. It is
assumed this
temperature will
closely match the user
input.
GIVEN / ASSUMED VALUES
Rcon = 0.077 m2-K/W
...as in EngRef which
co-insides closely to
values in 90.1 Table
A3.1B
Rfilm_in = 0.14 m2·K/W
...which is the
average of the 0.11
m2·K/W for heat flow
up and 0.17 m2·K/W for
heat flow down as per
90.1 A9.4.1...this
differs from EngRef!
Rfilm_out = 0.03 ...
as per EngRef and 90.1
A9.4.1 for all
exterior facing up or
sideways surfaces...NB
not for external
floors
k_soil = 1.30 W/m-K
...as per A6.1
LOOKUP VALUES
Insulation_configuration_best_fit_for_F-factor_from_Table_A6.3
(Perimeter_Insulation_is_Vertical,
Ins_mm, R-value)
CALCULATED VALUES
Soil_Heat_Flow_Path_Length
Rins
the rest
Someone may shed some
more light on how the
rating values were
calculated so that we
can back calculate the
U-value of the slab
construction.
Kind regards,
Jean.
On 19 April 2013
08:50, Jean Marais
<jeannieboef@xxxxxxxxx>
wrote:
Thanks Mike, I will
check the handbook and
see if revers
calculatiosn can bring
some light.
Funny thing that
definition...the
definition is aimed at
slabs that lay exposed
above the grade line
and are exposed to the
OD environment (that
means that their is no
requirement for
basement slabs!, i.e.
for basement slabs the
baseline is modeled as
proposed case), but
includes "or is less
than or equal to 600
mmj below the final
elevation of the
nearest exterior
grade".
If I learn anything
more, I'll post it.
Kind regards,
Jean.
On 18 April 2013
17:46, Michael J Witte
<mjwitte@xxxxxxxx> wrote:
Jean:
Just to clarify, for
"slab-on-grade" the
slab edge is exposed
to the air (directly
or through
insulation). From
Std. 90.1 Appendix A,
section A6.1 "For the
purpose of Section
A1.2, the base
assembly is a slab
floor of 6 in.
concrete poured
directly on to the
earth, the bottom of
the slab is at grade
line, . . ."
It seems there are
several issues here.
1. How to convert
from F-factor to
equivalent U-value.
This is what your
users need to know,
regardless of how
F-factor has been
implemented or
documented in
EnergyPlus. There
appears to be some
guidance here, but I
do not have access to
my handbook at the
moment to check this:
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-March/003573.html
2. The second issue
is whether EnergyPlus
has implemented and
documented the
f-factor model as
intended. I don't
have the answer to
that at the moment.
What I can tell you is
that the source code
matches the v8.0
documentation. It
creates two material
layers (which you
should be able to
report in the eio
output using
Output:Constructions).
Concrete layer (inside
layer):
! Add the 6" heavy
concrete for
constructions defined
with F or C factor
method
IF
(TotFfactorConstructs
+ TotCfactorConstructs
>=1 ) THEN
MaterNum =
MaterNum + 1
Material(MaterNum)%Group=RegularMaterial
Material(MaterNum)%Name
= '~FC_Concrete'
Material(MaterNum)%Thickness
= 0.15d0 ! m,
0.15m = 6 inches
Material(MaterNum)%Conductivity
= 1.95d0 ! W/mK
Material(MaterNum)%Density
= 2240.0d0 ! kg/m3
Material(MaterNum)%SpecHeat
= 900.0d0 ! J/kgK
Material(MaterNum)%Roughness
= MediumRough
Material(MaterNum)%AbsorpSolar
= 0.7d0
Material(MaterNum)%AbsorpThermal
= 0.9d0
Material(MaterNum)%AbsorpVisible
= 0.7d0
NominalR(MaterNum)
=
Material(MaterNum)%Thickness
/
Material(MaterNum)%Conductivity
Material(MaterNum)%Resistance
= NominalR(MaterNum)
Rcon =
Material(iFCConcreteLayer)%Resistance
The second layer is
the insulation layer
(outside layer) with
Rfic:
Reff = Area /
(PerimeterExposed *
Ffactor) - Rfilm_in -
Rfilm_out
Rfic = Reff -
Rcon
! ASHRAE Handbook
Fundamental 2005
!Thermal resistance
of the inside air
film, m2.K/W. Average
of 0.14 (heat flow up)
and 0.11 (heat flow
down)
REAL(r64),PARAMETER
:: Rfilm_in = 0.125d0
!Thermal
resistance of the
outside air film used
in calculating the
Ffactor, m2.K/W.
0.17/5.678
REAL(r64),PARAMETER
:: Rfilm_out = 0.03d0
Looking at example
file
1ZoneUncontrolled_FCfactor_Slab_UGWall.idf
Construction:FfactorGroundFloor,
slabconst,
!- Name
0.12,
!- F-Factor {W/m-K}
232.26,
!- Area {m2}
61.0;
!- PerimeterExposed
{m}
! <Material CTF
Summary>,Material
Name,Thickness
{m},Conductivity
{w/m-K},Density
{kg/m3},Specific Heat
{J/kg-K},ThermalResistance
{m2-K/w}
Material CTF
Summary,~FC_Insulation_1,
0.0000,
0.000,
0.000, 0.000,
31.50
Material CTF
Summary,~FC_Concrete,
0.1500,
1.950,
2240.000,
900.000, 0.7692E-01
When the Ffactor
surface heat balance
is done, the inside
convection coefficient
is varying as it does
for any surface in
EnergyPlus. This
seems reasonable.
However, the outside
surface temperature is
set directly to the
current value of
Site:GroundTemperature:FCfactorMethod,
so there is no outside
film coefficient
resistance during the
simulation. This
makes me question
whether Rfilm_out
should be dropped from
this equation:
Reff = Area /
(PerimeterExposed *
Ffactor) - Rfilm_in -
Rfilm_out
And as you ask, where
did the values for
Rfilm_in and Rfilm_out
come from? Do they
match the ASHRAE
f-factor
calculations.
3. Finally, is the
DesignBuilder team
planning to implement
the F and C-factor
option?
Mike
On 4/18/2013 1:08 AM,
Jean Marais wrote:
Hi Linda,
Mr. Hong is not
responding...
Sorry. This issue is
not going away. As
stated, yes, the
documentation has
changed in v8, but
still refers to air on
the outside of the
slab and no soil is
mentioned, i.e.
"Q = Area * Ueff *
(Tair,out – Tair,in) =
(Tair,out – Tair,in) *
(Pexp * F-factor)",
"Tair,out is the
outside air
temperature in °C",
"The outside air film
resistance Rfilm, out
= 0.03 m2·K/W.", etc.
If a slab is
"on-grade" then I fail
to see how air_outside
can factor into the
equation. Mr. Hong has
insinuated that these
issues have been
corrected "The air
film (either inside or
outside) is not
included in the
calculation of
effective U-factor.
The soil layer is
modeled as part of the
6" concrete and an
insulation layer to
come up with the
equivalent U-factor.",
but the documentation
of the last v8 release
does not reflect it.
As I am supporting
DesignBuilder, and
DesignBuilder does not
currently support the
F-factor objects for
e+, it is important
for me to explain to
clients how to
calculate the Ueff to
properly reflect the
f-factors in 90.1. No
one has been able to
explain this to me. I
need to know what
R-soil ASHRAE was
using for these
f-factors AND which
film factors (if any)
are included in the
f-ractor rating
values.
This information would
help many users who
have been ignoring
this issue for many
years. I'm always
supprised how long
people have been
"conforming" to ASHRAE
90.1 for simulations.
Kind regards,
Jean
On 17 April 2013
14:51, Linda Lawrie
<linda@xxxxxxxxxxxxxx> wrote:
I presume he meant the
current V8 release.
But I'm not sure.
At 11:21 PM 4/16/2013,
jeannieboef@xxxxxxxxx wrote:
May I ask for your
source of information?
Do you mean the next
release, as the v8
documentation includes
the film resistances?
Kind regards,
Jean
Sent from my iPhone
On 16.04.2013, at
22:36, Tianzhen Hong
<thong@xxxxxxx> wrote:
Jean,
We clarified the
documentation in the
coming E+ 8.0 release.
The air film (either
inside or outside) is
not included in the
calculation of
effective U-factor.
The soil layer is
modeled as part of the
6" concrete and an
insulation layer to
come up with the
equivalent U-factor.
Tianzhen
To: linda@xxxxxxxxxxxxxx
Subject: [EnergyPlus
!7333]: F-factor
method
engineeringreference
documentation error?
Date: Wed, 10 Apr 2013
09:39:30 +0000
Jean Marais updated
#7333
-------------------------
F-factor method
engineeringreference
documentation error?
---------------------------------------------------------
Ticket ID: 7333
URL: http://energyplus.helpserve.com/staff/Tickets/Ticket/View/7333
Full Name: Jean Marais
Email: jeannieboef@xxxxxxxxx
Creator: User
Department: General
Staff (Owner): --
Unassigned --
Type: Issue
Status: Open
Priority: Medium
Template Group:
Default
Created: 10 April 2013
09:39 AM
Updated: 10 April 2013
09:39 AM
Due: 11 April 2013
09:39 AM (1d 0h 0m)
Resolution Due: 12
April 2013 09:39 AM
(2d 0h 0m)
Dear Team,
How can there be an
air-resistance-film on
the underside of the
slab? I am comparing
to DOE-2E
http://www-esl.tamu.edu/docs/terp/2012/ESL-TR-12-02-01.pdf
Surely a soil layer
should be assumed
here. And then which
soil layer was used
for the F-factors
listed in ASHRAE 90.1?
Please advise.
Kind regards,
Jean.
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|