You are using a vav with reheat, right. In clg mode it will reheat to the zone htg setpoint not the zone clg setpoint.

Sent from my iPhone (excuse the brevity)
Mit freundlichen Grü�en

i. A.
Jean Marais
B.Eng (Mech)
LEED Accredited Professional
Building Energy Modeling with DesignBuilder and EnergyPlus

b.i.g. bechtold
INGENIEURGESELLSCHAFT MBH
KeithstraÃ?e 6
10787 Berlin
Tel.   +49 30 6706662-23
Fax  +49 30 6706662-18
Firmensitz: Berlin, Registergericht: Amtsgericht Charlottenburg, HRB 112242 B
Geschäftsführer: Bernd Bechtold, Tino Laupitz, Carsten Teichmann

"The LEED® (Leadership in Energy and Environmental Design) Green Building
Rating System is the nationally accepted benchmark for the design, construction,
and operation of high performance green buildings."
Other LEED descriptive copy may be found on the USGBC Web site: http://www.usgbc.org/leed

Official Reseller for DesignBuilder in Germany and Austria
 


On 12.06.2013, at 03:37, Patrick Bivona <patrick.bivona@xxxxxxxxx> wrote:

 

Hi,

I'm getting this warning message after a run:

   ** Warning ** SizeZoneEquipment: Supply air temperature (calculated) within 5C of zone setpoint temperature
   **   ~~~   ** ...check zone thermostat set point and design supply air temperatures
   **   ~~~   ** ...zone = "ZONE 1F ENTRANCE WEST" first occurrence during cooling load calculations
   **   ~~~   ** ...predicted zone cooling load = -863.19 W
   **   ~~~   ** ...zone temperature            = 20.00 C
   **   ~~~   ** ...supply air temperature      = 16.00 C
   **   ~~~   ** ...temperature difference      = -4.00000 C
   **   ~~~   ** ...calculated mass flow rate   = 0.21163 kg/s

I understand the general purpose of the temperature difference check: avoid high flow rates.
What I don't understand is why the "zone temperature" is reported as being 20 degC, when my thermostat cooling setpoint is 24 degC.

Am I wrong in assuming that "zone temp" should be the cooling setpoint? If so, why recommend to check the zone thermostat in the warning message?

I'm confused!

Thanks in advanced for your help,
Patrick Bivona



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___