[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Autosizing dx cooling coil is under sizing minimum flowrate at maximum load
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Autosizing dx cooling coil is under sizing minimum flowrate at maximum load
- From: "Jean marais" <jeannieboef@xxxxxxxxx>
- Date: Wed, 12 Jun 2013 06:18:39 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 12 Jun 2013 00:19:07 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1371017945; bh=DcVFvczRkkIDJdh5CGPir4KrRvf95MNxePOdy6vmaiY=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=oai+vS+8aBOT98VMW+t0C5u6ulQ3Ylnm4ihraZYIpfrIqg2nNbtWXAot13YlLyuPAuhySsf73W590aibrQ/LRcnUu5hebHJyHXg8IbODIXGt7rYtjM8cNbUg17BE9dB3+dBjHKRP3/n4TGwUQWlpRb7+sk4K/6dADxFxscpnK4M=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=F64DHjJ3LpwC5VnwasObPjdkPyx6AKWhj872+459QD9NuVV7T3dyq/fdb9Symh0Dfci8RKivZcISzLdRlixVopNbAbSCsm7sFFU7q6za3jCCOxCHY/35aCt3t/5DUVhkD8ZKG6h7ZfXL3Ljg84MId8SZ2Q5czn22Rrs4rgKP87E=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear Group,
Is anyone else experiencing this:
Autosizing dx cooling coil is under sizing minimum flowrate at maximum load
Here is an example of my coil:
Coil:Cooling:DX:SingleSpeed,
118443 AHU Cooling Coil, !- Name
SchCpct_LowTempClgOFF, !- Availability Schedule Name
autosize, !- Rated Total Cooling Capacity {W}
autosize, !- Rated Sensible Heat Ratio
3.81, !- Rated COP {W/W}
autosize, !- Rated Air Flow Rate {m3/s}
, !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)}
118443 AHU Gas Heating Coil Outlet, !- Air Inlet Node Name
118443 Unitary Unit Outlet, !- Air Outlet Node Name
118443 AHU DX Coil Cap-FT, !- Total Cooling Capacity Function of Temperature Curve Name
118443 AHU DX Coil Cap-FF, !- Total Cooling Capacity Function of Flow Fraction Curve Name
118443 AHU DX Coil EIR-FT, !- Energy Input Ratio Function of Temperature Curve Name
118443 AHU DX Coil EIR-FF, !- Energy Input Ratio Function of Flow Fraction Curve Name
118443 AHU DX Coil PLF, !- Part Load Fraction Correlation Curve Name
1000, !- Nominal Time for Condensate Removal to Begin {s}
1.5, !- Ratio of Initial Moisture Evaporation Rate and Steady State Latent Capacity {dimensionless}
1, !- Maximum Cycling Rate {cycles/hr}
45, !- Latent Capacity Time Constant {s}
118443 AHU Cooling Coil Condenser Inlet, !- Condenser Air Inlet Node Name
AirCooled, !- Condenser Type
0, !- Evaporative Condenser Effectiveness {dimensionless}
, !- Evaporative Condenser Air Flow Rate {m3/s}
0, !- Evaporative Condenser Pump Rated Power Consumption {W}
0, !- Crankcase Heater Capacity {W}
10; !- Maximum Outdoor Dry-Bulb Temperature for Crankcase Heater Operation {C}
********************************
Reporting the output temps on a timestep basis at 60 steps per hour, I see wildly fluctuating temps from minute to minute by more than 2 deg C, although the Setpoint is Constant.
This is causing all sorts of error messages. For example:
** Warning ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed "118288 AHU COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = 1.53 C.
** ~~~ ** ...Occurrence info = KITA, 03/27 12:36 - 12:37
** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil
** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 17.430 C.
** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs.
** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.
*****************************and
** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for 118320 AHU, at KITA, 01/01 00:17 - 00:18
*****************************and
** Warning ** SimHVAC: Maximum iterations (100) exceeded for all HVAC loops, at KITA, 01/21 13:35 - 13:36
** ~~~ ** The solution for one or more of the Air Loop HVAC systems did not appear to converge
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on each max iteration exceeded.
**********************
My minimum airflow rates are autosized to meet sensible load.
Any comments please.
Jean
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/