Re: [EnergyPlus_Support] Cooling and Heating Coil





Thank you very much for you response



On Thu, Jun 13, 2013 at 12:46 PM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

You don't specify the refrigerant properties. You instead specify the
air-side performance through the use of performance curves. Read the
EngineeringReference for Single-Speed Electric DX Air Cooling Coil and
the InputOutputReference for Coil:Cooling:DX:SingleSpeed. Example files
will show you how to connect the required fan and coil objects to the
unitary system, see FurnaceWithDXSystem.idf as a start.



On 6/12/2013 7:35 PM, yiolari87 wrote:
> Dear Group,
>
> I need a clarification about the simulation of a split system air conditioning system. When a DX cooling or heating coil is used, the connection between the indoor and outdoor unit is described by the use of a refrigerant? How can I set the properties of this refrigerant?
>
> Thank you in advance
> George Georgiou
>
>
>
> ------------------------------------

>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 50 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___