So because the minimum efficiency criteria in 90.1 (and possibly manufacturer data sheets) are given in P-I units "SEER" value or SI units "SCOP", it would make life easier if the program input fields could take this and back calculate the dx coil COP, instead of the other way round. Is this possible?

At the same time 90.1 requires the fan energy be slit out so that part is nicely handled the way it is set up now.

However, itteratively changing COP inputs to arrive at the required SEER values in the output reports, is surely a sub-optimal use of time. Is there a better way?

Yes, James has released an impressive spread sheet on the matter, but an automated solution would be best. Also, I don't remember his spread sheet actually spitting out a calculated value...

Point is my current project has 29 different units each autosizing fan sizes and from the required power, require a specific minimum SEER value to be hit. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Aymeric Novel <nanabush@...> wrote:
>
> Hi,
> 
> I sas you sent your warnings/errors summary already and that you got good guidances from the forum. Follow them step by step, your model will be cleaner.
> 
> Then, from my experience, your warnings about surfaces are quite,typical from design builder generation. Correct them as advised by forum. The DX coil airflow issue is just due to wrong auto size in DX coil object. The parameter in m3/s/kW has to be set within the interval accepted by energyplus. This interval is specified in the IDF and in the engineering reference PDF. 
> 
> Also, refer to four. Discussions about the COP definition. Indeed it is quite tricky that the COP definition I the 90.1 standard is based on AHRI definition while within Eplus the definition is different. You must take it into account. The reviewer will check this table in your summary and see if your AHRI corrected COP matches the 90.1 standard value for the baseline model.
> 
> Best regards,
> Aymeric
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/