[EnergyPlus_Support] Re: G3.1.3.13 of ASHRAE 90.1-2007
My appologies...I was thinking of G3.1.3.14. For G3.1.3.13 Karen is correct. However, as the minimum setting is input in m3/s, you'll have to work this out for each zone or automate the input with perhaps a macro.
The ODAmin should take care of itself (see Damper Heating Action), if a Design Specification Outdoor Air Object Name is also specified.
I think the 2.15L/s/m2 minimum applies all of the time. This you may want to run by the LEEDuser forum for a second opinion.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Karen Walkerman <kwalkerman@...> wrote:
>
> I don't think that the minimum setpoint is meant to be time dependent - I
> think the minimum volume setpoint is "2.15 l/s*m^2 of floor area served or
> the minimum ventilation rate, whichever is larger" either all the time, or
> only during occupied hours, and the 0 during unoccupied hours.
>
> --
> Karen
>
>
> On Mon, Aug 26, 2013 at 12:59 PM, Jean marais <jeannieboef@...> wrote:
>
> > **
> >
> >
> > I love it when you post these questions about Appx G. It blatantly points
> > out how sections of it have been consistantly ignored by both users and
> > reviewers since at least 2004 (when many of the possibilities of today
> > weren't even there).
> >
> > There is no "built-in" way to deal with this, and I have luckly not had a
> > system 8 yet. If I had to do it now, I would most likely turn to EMS.
> >
> > Let us know how you decide.
> >
> > Jean
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/