|
I would recommend *not* using the Common Pipe Simulation in the PlantLoop object. The relatively new HeatExchanger:FluidToFluid is able to reliably connect two separate plant loops together and can be controlled. With this heat exchanger you would have two separate Plant Loops, one for primary and one for secondary (or even multiple secondary loops). There are no limitations for variable speed pumps with this approach. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of andresdagm@xxxxxxxxx Hi, all group, i need some help! I got this warning when i try to simulate a Primary and secondary both variable pumps in Chiller water systems (The chiller incorporate VFD): ** Warning ** SetupCommonPipes: detected variable speed pump on supply inlet of TwoWayCommonPipe plant loop It seems that Commonpipesimulation in Plant Loop doesn't simulate primary and secondary variable pumps. There is any way to could model primary and secondary variable pumps?? Thank you, Dante Garcia __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |