The WinterDesignDay is not a day of the week. All other schedules define, explicitly or implicitly, what there values must be on the designday used to size the equipment. For example, if your lighting schedule is zero for allotherdays and you did not specify a winterdesignday entry field, then it will use zero. Another important implied object and field is the sizing:parameter object. Check it out. Hope that helps, Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.