Jean, Alberto and Jim,
thanks for helping me, but the error persist. I'm sending the idf model. Perhaps you able to view the error easily. I'm actually don't know why this is happening. It's the first time i'm seeing this. Thanks a lot for this! Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor em Eficiência Energética LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Mon, 9 Sep 2013 06:16:06 -0500 Subject: RE: [EnergyPlus_Support] Controller Error Respectfully disagreeing ?. HVAC Cooling coils are always reverse action. This is specified in the Controller:WaterCoil object (example below). I do not recall all of the several ways that I have erred in order to receive this message, but I think improper setpoints are the most common. Your 12.8C setpoint looks OK, but perhaps there is a zone setpoint that is improper?
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Alberto Hernandez Neto - USP
Dear Ivan,
You should change the status of reverse action of the colling coil controller .
Regards,
Alberto Hernandez Neto
De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Em nome de Ivan Mezzacapa
Hi!
i don't know how solve this problem. Someone could help me?
Thanks!!
** Severe ** FindRootSimpleController: Controller error for controller = "FC-3P-A-01 COOLING COIL CONTROLLER" ** ~~~ ** Environment=Sao Paulo -TRY WMO#=, at Simulation time=01/16 08:00 - 08:15 ** ~~~ ** Controller function is inconsistent with user specified controller action = "" action ** ~~~ ** Actuator will be set to maximum action ** ~~~ ** Controller control type=Temperature ** ~~~ ** Controller temperature setpoint = 12.80 [C] ** ~~~ ** Controller sensed temperature = 25.78 [C] ** ~~~ ** Controller actuator mass flow rate set to 4.27 [kg/s] ** ~~~ ** Controller actuator temperature = 26.10 [C] ** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled ** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature ** ~~~ ** Note: Hot water coils should be normal action and the entering hot ** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor em Eficiência Energética LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326 __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.