Yes, having two water coils on the same plant branch is going to cause problems. A heating coil needs to be connected to a hot water plant loop and a cooling coil needs to be connected to a chilled water plant loop. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of stagiaire3@xxxxxxxx Thank you Brent, In fact, I don't have any unitary system, but your contribution makes me think that the problem may come from two controllers on the same water branch. Could it be possible? If that is the case, I don't really know what to do: from what I've seen so far, E+ does not allow water coil without controller... (In my model, the second controller is inefficient (convergence tolerance set to 100°C) since the heating coil water flow rate must be determined by the cooling coil flow rate only). On top of that, I did not find a way to regroup both cooling and heating coil in only one cooling coil (thus having only one controller) because the air input and output conditions of this "coil system" would be inconsistent with E+ water coil definition : I would get "no apparatus dew-point found" errors... (input condition: 27°C, 15g/kgas, ouput condition: 20°C, 7g/kgas) What do you think?
I have seen this sort of thing happen when the input for water coil’s control is set up with both a Unitary system and a Controller:WaterCoil. It needs to be one or the other but not both. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of stagiaire3@... I must add that this is not only a report problem. With total water coil cooling coil rate and input/output water temperature, I could do the math to determine water flow rate... The point is that I have 70kW total cooling coil rate, and 0kW chiller electric power, so the 0m3/s water flow rate is really accounted by E+... Hoping this could help understanding my problem, Luc
Dear community, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |