Dear all,
Thank you very for replying my post.
I notice there is a rounded issue when ASHRAE generates SI edition for IP edition. To avoid this issue (sorry I do not have all documents needed in IP edition, so I still try to use SI to explain my question further), I hand calculate surface resistance figure and others: interior surface resistance 0.10743 (R-0.61 IP), exterior surface resistance 0.02994 (R-0.17 IP). Use roofs - insulation entirely above deck climate zone 4 as example:
. Nonresidential Residential Semiheated
IP units U-0.048 R-20.0ci U-0.048 R-20.0ci U-0.173 R-5.0ci
SI units (cal.) U-0.27256 R-3.5220 U-0.27256 R-3.5220 U-0.98234 R-0.88055
It would be fine to use both methods (will not see big difference between the two) when metal deck is used because on page 77 in Standard 90.1 2007 SI edition section A2.21, it states "R-0 for metal de
Dearl all,
In ASHRAE Standard 90.1 2007 SI Edition, Page.18, it states:
5.5.3 Opaque Areas. For all opaque surfaces except doors, compliance shall be demonstrated by one of the following two methods:
1. Minimum rated R-values of insulation for the thermal resistance of the added insulation in framing cavities and continuous insulation only. Specifications listed in Normative Appendix A for each class of construction shall be used to determine compliance.
2. Maximum U-factor, C-factor, or F-factor for the entire assembly. The values for typical construction assemblies listed in Normative Appendix A shall be used to determine compliance.
Attachment not found: d:\eudora\attach\comparison roofs insulation entirely above deck Assembly U calculation.PNG