In DesignBuilder I create small subsurfaces in correspondence of the thermal bridges. The subsurfaces have a higher thermal transmittance than the normal surfaces. I calculate the modified thermal transmittance in order to have the correct heat flow in stationary conditions.


heat flow considering the thermal bridge = heat flow considering the subsurface


psi * h + UA = U1 * A1 + U * (A-A1)


where psi is the thermal bridge coefficient, h is the length of the thermal bridge, U is the thermal transmittance of the wall in "normal" conditions, A is the total area of the wall, U1 is the thermal transmittance of the subsurface and A1 its area


I suggest the article of Martin et al. "Problems in the calculation of thermal bridges in dynamic conditions": http://www.sciencedirect.com/science/article/pii/S0378778810003701

Best Regards




---In energyplus_support@xxxxxxxxxxxxxxx, <zupfera@...> wrote:

Hi all,

when entering the construction of the external walls the


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___