Re: [EnergyPlus_Support] Re: Heat recovery





Thank you sir for help me

Actually the load on each AHU is different and other issue is when the load on any AHU is changes i can not control the outdoor air because it also connected to the other AHUs.
I already tried with duct with splitter and mixer but it create some problem. I think there may be a solution with ducting splitter and mixer but i couldn't find out.  



On Sunday, 3 November 2013 1:25 AM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 
Yasin Khan,
The simplest solution is probably to provide one heat recovery heat exchanger on each AHU.  Each such HX should have the capacity and fan power of 1/3 of the actual HX.
I think it is possible to supply air from a single HX to three AHUs, but I have not done so.
 
 
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
 
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of yasin khan
Sent: Saturday, November 02, 2013 12:47 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Heat recovery
 
 
Can anybody help me in my modeling ?
As I already shared my problem that i couldn't coupled a heat recovery unit with 3 AHUs.
 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___