yes, the bypass is there! I guess I have found the issue. I hard-sized (oversizing a lot) the heating coil..if now I use the autosize everything is fine
Dear users,
I am getting an error saying that the water temperature in HW plant loop is getting too hot, and the simulation fails. I have read few other conversations on this topic, but I hope that someone has some more tips.
I believe that there is something wrong with the pump (constant speed), also because I can solve the issue by replacing the constant speed pump with a variable speed pump.
But theoretically it should also work with the constant speed operating as an on/off system. Any clue?