Zane, Splitting the Zone is perfectly viable. Just be aware of the limitations. 1) direct solar radiation (beam) does not pass through interior vitual partition "windows". 2) air mixing between zones must be user defined. 3) other considerations probably exist, but don't come to mind so early in the morning For both options, it is preferable to run a CFD simulation to help "tune" the energyplus simulation. I use DesignBuilder for this. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.