[EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running simultaneously!?!?



Thank you very much, I will try and feedback.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Artem Zhukov <artem.zhukov@...> wrote:
>
> I would suggest use SetpointManager:SingleZone:Reheat as h/c coils manager.
> This manager do not allow coils works against each other.
> 
>  
> 
>  
> 
>  
> 
>  
> 
> 
> 
> 
> BR,
> 
> Artem Zhukov
> 
>  
> 
> HVAC Consultant/Building Simulation Engineer
> 
>  
> 
> Mob.: +420 774 081 898
> 
> SKYPE: zhukov_artem
> 
>  <http://cz.linkedin.com/pub/artem-zhukov/22/6b4/55> View LinkedIn profile
> 
>  <http://www.icalx.com/public/azhukov/Artem_Zhukov_Calendar.ics> Web Cal
> 
>  
> 
> TO PRINT OR NOT TO PRINT
> 
>  
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hisham.rashrash
> Sent: Monday, December 23, 2013 10:25
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx; EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running
> simultaneously!?!?
> 
>  
> 
>   
> 
> Thank you very much. I will try this and provide feedback.
> 
> EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx> , Germán Campos
> <ecoeficiente@ <mailto:ecoeficiente@> > wrote:
> >
> > Once expanded:
> > 
> > You have to use a "Cooling type Setpointmanager" with Min Temp=11 and Max
> > Temp=99 (one of those: SetpointManager:SingleZone:Cooling,
> > SetpointManager:MultiZone:Cooling:Average, SetpointManager:Warmest or
> > SetpointManager:WarmestTemperatureFlow) in the "XXX_VAVSYS Supply Fan
> > Outlet" node and a "Heating type Setpointmanager" with Min Temp=0 and
> > MaxTemp=33 (SetpointManager:SingleZone:Heating,
> > SetpointManager:MultiZone:Cooling:Heating)
> > in the "XXX_VAVSYS Supply Path Inlet" node.
> > 
> > Then verify that you have two SetpointManager:MixedAir:
> > 
> > One for the cooling water coil with:
> > 
> > Reference Setpoint Node Name: XXX_VAVSYS Supply Fan Outlet
> > Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
> > Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
> > Setpoint Node: XXX_VAVSYS Mixed Air Nodes
> > 
> > One for the heating water coil with:
> > 
> > Reference Setpoint Node Name: XXX_VAVSYS Supply Path Inlet
> > Fan Inlet Node Name: XXX_VAVSYS Heating Coil Outlet
> > Faon Outlet Node Name: XXX_VAVSYS Supply Fan Outlet
> > Setpoint Node: XXX_VAVSYS Heating Coil Outlet
> > 
> > Regards,
> > 
> > 
> > _______________________________
> > 
> > Germán Campos
> > 
> > *Aurea Consulting *
> > www.ecoeficiente.es <http://www.ecoeficiente.es> 
> > www.designbuilder.es <http://www.designbuilder.es> 
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/