Since the data that was used to classify climate zones in ASHRAE 90.1 is different from the data used to generate weather data file, it is no surprise that they do not agree. For choosing the climate zone for the envelope requirements and other requirements in 90.1, you should use the data that is provided with 90.1. When selecting a weather file for Appendix G, you should use the weather file for your location or "..select available weather data that best represent the climate at the weather site." The EnergyPlus report that calculates the climate zone based on the weather file is only an approximation and should not be used to select the climate zone for your location. As far as selecting the proper weather file, if possible choose one that is in the same location as the building you are modeling, if that is not possible, choose one that is close or as climatically similar as possible.
Jason
On 4/16/2014 7:45 AM, <mailto:seanking.1970@xxxxxxxxxxx>seanking.1970@xxxxxxxxxxx wrote:
> Dear all,
> I don't know if some of you are aware that there is sometimes (quite often though) the climate code read from E+ weather stat file does not meet the code from ASHRAE 90.1 standard climate zone tables.
> Sorry if you do not know what I am talking about, here comes the details:
>
> I am doing a LEED/ASHRAE 90.1 modelling in EnergyPlus, but bump into a problem which really puzzled me.
The proposed location of my building is in Rome, Italy, and the weather file I need to use is ITA_Rome.162420_IWEC.epw (downloaded from EnergyPlus website). However, when I check stat file, the climate zone code ("Climate type" shown in the file, see below) is "3C", whilst ASHRAE Standard 90.1 climate zone table indicates a code of "4".
Climate type "3C" (ASHRAE Standards 90.1-2004 and 90.2-2004 Climate Zone)
> I have therefore carried out some more checks on other weather files (based on different locations), although most cases are correct or close to 90.1 Standard, there does exist some differences. For example, Istanbul in Turkey shows "3C" in stat weather file instead of "4" in Standard 90.1, Las Vegas (Nevada, USA) shows "2B" rather than "5B" (very big difference!) and Seattle (Washington, USA) gets "4A" instead of "5B".
Could anybody please advise what possible reasons in generating these differences, and how to choose a right weather file to do a LEED/ASHRAE modeling if the codes are not consistent between the two? Thank you very much in advance.
> Best regards,
> Sean King
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection.� Limit attachments to small files.
EnergyPlus Documentation is searchable.� Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31746/stime=1397654653>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlaDlqNWI5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NzY1NDY1Mw-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmcWJvaWZjBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTc2NTQ2NTM->New Members 10
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkbTBzczhiBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk3NjU0NjUz><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
� <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy � <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe � <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___