Echoing what Jean and Jason said. . . do not use the climate zone in the .stat file. It should only be the climate zone from Standard 90.1 (data for 1961-1990) or the recently published ASHRAE Standard 169-2013 Climatic Data for Building Design Standards, which includes data up through 2008 and matches the 2009 ASHRAE Fundamentals design conditions (used in DDY if there's a location in the Fundamentals). Standard 169 includes maps of the entire world (at 1 deg lat x 1 deg long resolution) as well as a climate zone for each location in the 2009 Fundamentals.
Note that locations in Standard 169-2013 tended to move to lower (hotter) climate zones. And there's a new Climate Zone 0 that covers the hottest locations worldwide -- none are in the US.
There's an update in progress to bring Standard 169 up to date with data from the 2013 Fundamentals design conditions.
On Wed, Apr 16, 2014 at 9:21 AM, <mailto:jeannieboef@xxxxxxxxx>jeannieboef@xxxxxxxxx <<mailto:jeannieboef@xxxxxxxxx>jeannieboef@xxxxxxxxx> wrote:
> Â
Don't use the stat file's classification for anything other than an idea of the weather. The stat file contains statistics based on the weather file, not the actual raw weather data from the last 60 years. The same applies to the ddy designday. These should be from ASHRAE. If they have been produced from the weather file (itself a statistical file), then they should be used with caution and not for code compliance (which is the case if they are created with the weather converter utility).
>
> Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
> i. A.
Jean Marais
b.i.g. bechtold
Tel. Â <tel:%2B49%2030%206706662-23>+49 30 6706662-23
> On 16.04.2014, at 14:45, <<mailto:seanking.1970@xxxxxxxxxxx>seanking.1970@xxxxxxxxxxx> wrote:
>
>> Â
Dear all,
>>
>> I don't know if some of you are aware that there is sometimes (quite often though) the climate code read from E+ weather stat file does not meet the code from ASHRAE 90.1 standard climate zone tables.
>> Sorry if you do not know what I am talking about, here comes the details:
>>
>> I am doing a LEED/ASHRAE 90.1 modelling in EnergyPlus, but bump into a problem which really puzzled me.
Â
The proposed location of my building is in Rome, Italy, and the weather file I need to use is ITA_Rome.162420_IWEC.epw (downloaded from EnergyPlus website). However, when I check stat file, the climate zone code ("Climate type" shown in the file, see below) is "3C", whilst ASHRAE Standard 90.1 climate zone table indicates a code of "4".
Â
Climate type "3C" (ASHRAE Standards 90.1-2004 and 90.2-2004 Climate Zone)
>> I have therefore carried out some more checks on other weather files (based on different locations), although most cases are correct or close to 90.1 Standard, there does exist some  differences. For example, Istanbul in Turkey shows "3C" in stat weather file instead of "4" in Standard 90.1, Las Vegas (Nevada, USA) shows "2B" rather than "5B" (very big difference!) and Seattle (Washington, USA) gets "4A" instead of "5B".
Â
Could anybody please advise what possible reasons in generating these differences, and how to choose a right weather file to do a LEED/ASHRAE modeling if the codes are not consistent between the two? Thank you very much in advance.
>> Best regards,
>> Sean King
>
>
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31751/stime=1397663965>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJldjYwOWpwBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NzY2Mzk2NQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmbGtjOGdkBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTc2NjM5NjU->New Members 11
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkcjZwODl0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk3NjYzOTY1><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___