Re: [EnergyPlus_Support] Problem with UpdateZoneSizing: Heating supply air temperature
Hi Marco,
Now that your Sizing:system object is correct, the componants won't be sized to a ridiculously huge airflow as calculated by the sizing:zone object. E+ could look at adjusting the current warning which would only be relevant when the sizing:system object is sizing on sensible loads, i.e. taking the Sizing:Zone calculated airflow rates and applying them to all the componants for sizing. Just ignore the warning. Or use the flow/limit option in the sizing:zone object and see if that makes a difference.
Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
On 02.05.2014, at 19:43, Marco Aldegheri <<mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx> wrote:
>
> Well, I did a bit of confusion... this schedule is wrong.
> I didn't understand if the 1st one is correct, what about the definition of summerdesignday and winterdesignday? They are not explicit in the time definition... Is that the problem?
>
>
> On Friday, May 2, 2014 4:40 PM, Marco Aldegheri <<mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx> wrote:
> But in this way, the winterdesignday and the summer design day should be included in each periods... a schedule like this one could be better?
>
> Schedule:Compact,
> P4:P4%A2Zn1k Heating Setpoint Schedule, !- Name
> Temperature, !- Schedule Type Limits Name
> Through: 22 Apr, !- Field 1
> For: SummerDesignDay, !- Field 2
> Until: 24:00, !- Field 3
> -50, !- Field 4
> For: WinterDesignDays AllOtherdays, !- Field 2
> Until: 07:00, !- Field 3
> 16, !- Field 4
> Until: 08:00, !- Field 5
> 20, !- Field 6
> Until: 12:00, !- Field 7
> 16, !- Field 8
> Until: 14:00, !- Field 9
> 20, !- Field 10
> Until: 19:00, !- Field 11
> 16, !- Field 12
> Until: 23:00, !- Field 13
> 20, !- Field 14
> Until: 24:00, !- Field 15
> 16, !- Field 16
> Through: 8 Oct, !- Field 17
> For: SummerDesignDay, !- Field 2
> Until: 24:00, !- Field 3
> -50, !- Field 4
> For: WinterDesignDays AllOtherdays, !- Field 2
> Until: 07:00, !- Field 3
> 16, !- Field 4
> Until: 08:00, !- Field 5
> 20, !- Field 6
> Until: 12:00, !- Field 7
> 16, !- Field 8
> Until: 14:00, !- Field 9
> 20, !- Field 10
> Until: 19:00, !- Field 11
> 16, !- Field 12
> Until: 23:00, !- Field 13
> 20, !- Field 14
> Until: 24:00, !- Field 15
> 16, !- Field 16
> Through: 8 Oct, !- Field 17
> For: AllDays, !- Field 18
> Until: 24:00, !- Field 19
> -50; !- Field 20
> On Friday, May 2, 2014 4:10 PM, Jean Marais <<mailto:jeannieboef@xxxxxxxxx>jeannieboef@xxxxxxxxx> wrote:
>
possibly...AllDays includes the winter and the summer designdays which sets the setpoint at -50. heating setpoints less than 0 get rounded to 0 by the program as per the idd.
>
>
> 2014-05-02 15:54 GMT+02:00 Marco Aldegheri <<mailto:m.aldegheri@xxxxxxxxx><mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx>:
>>
>>
>>
>> Well Jean, you explainaition was really clear.
>>
>> Anyway, about the setpoint schedule manager, it was created by DesignBuilder.
>> I would remember you that I have only heating.
>>
>> For each zone I find that in E+ a dualsetpoint is created like this:
>>
>> !- =========== ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========
>>
>> ZoneControl:Thermostat,
>> P0:P0%A1Zn5i Thermostat, !- Name
>> P0:P0%A1Zn5i, !- Zone or ZoneList Name
>> 48, !- Control Type Schedule Name
>> ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
>> P0:P0%A1Zn5i Dual SP; !- Control 1 Name
>>
>> where
>>
>> ! Schedule: Control type schedule: Always 4
>> Schedule:Compact,
>> 48, !- Name
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31861/stime=1399139444>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlMjhyM2dvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5OTEzOTQ0NA-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNm9jYmQ5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTkxMzk0NDQ->New Members 11
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkNDcxZWd0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk5MTM5NDQ0><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___