[EnergyPlus_Support] Severe Error occuring in the simulation



Hello !

I want to simulate a 3 Zone Building with my own regulation in HVAC. The programm do correctly the simulation, but at the end, I have a severe error occuring 800 time :



** Severe  ** FindRootSimpleController: Controller error for controller = "REGEN COIL CONTROLLER"

   **   ~~~   **  Environment=PERIODE SIMU, at Simulation time=03/16 14:50 - 15:00

   **   ~~~   **   Controller function is inconsistent with user specified controller action = Normal action

   **   ~~~   **   Actuator will be set to maximum action

   **   ~~~   ** Controller control type=Temperature

   **   ~~~   ** Controller temperature setpoint = 95.00 [C]

   **   ~~~   ** Controller sensed temperature = 13.46 [C]

   **   ~~~   ** Controller actuator mass flow rate set to 1.65 [kg/s]

   **   ~~~   ** Controller actuator temperature = 13.46 [C]

   **   ~~~   **   Note: Chilled water coils should be reverse action and the entering chilled

   **   ~~~   **         water temperature (controller actuator temperature) should be below the setpoint temperature

   **   ~~~   **   Note: Hot water coils should be normal action and the entering hot


   **   ~~~   **         water temperature (controller actuator temperature) should be above the setpoint temperature



Can you help me to understand what kind of problem I have here, please ?



Thanks !





__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31915/stime=1399645615>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlaTMwdmsxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5OTY0NTYxNQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmcnZidm82BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTk2NDU2MTU->New Members 11
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkMjVxcmdrBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk5NjQ1NjE1><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___