I think your floor heater refers to the lowtemperatureradiant object. There are two versions: constantflow (variable supply temperature) and variableflow (constant supply temperature).
The first model inherrently mixes the return water temperature to the supply water to attain required supply temperature to satisfy the load at constant flowrate for the radiant tubing. This is "inside" the model and you can't really see the model internal node temperatures. It basically has the tempering built in.
The second model is fed with a set temperature (you can put a setpoint manager here to do this). The model will demand more or less flow depending on the load and the supply temperature should be kept as per the setpoint manager.
In both models the return temperature will vary because the system has a capacity to meet design loads at design conditions and the conditions of both radiant surface temperatures and room air temperatures effect the convection coefficients and hence the heat transfer characteristics.
Setting up a constant heat transfer system (constant water dT) is probably possible, but would require an EMS to dynamically adjust a temperature setpoint or mass flowrate as well as a system with enough capacity.
Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
On 13.06.2014, at 13:25, "<mailto:lepinole@xxxxxxxxx>lepinole@xxxxxxxxx [EnergyPlus_Support]" <<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
>
> Dear colleagues,
>
>
> I am trying to simulate a heating system that includes solar storage tank, condensing boiler and floor heater. I am wondering if it is possible to control the water flow from the floor heater and solar storage tank depending on the difference between the outlet water temperature of the floor heater and the outlet water temperature of the solar storage tank. Precisely, is it possible to say EnergyPlus that when the outlet water temperature of the floor heater is warmer than the outlet water temperature of the solar storage tank the all flow (from floor heater) goes directly to the boiler not in the storage tank. Contrary, when the outlet water temperature of the floor heater is colder than the outlet water temperature of the solar storage tank the all flow (from water heater) goes to the the storage tank. I know there is a tempering valve object but it can be used only in situation when the outlet water temperature from the tank is too high.
>
>
> In a hope that someone will answer and help me I thank You in advance.
>
>
>
>
>
> Novak Nikolic, research assistent
>
>
>
__._,_.___
Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=32251/stime=1402733097>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlMmdmcXE4BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQwMjczMzA5Nw-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmdnY5NTRjBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0MDI3MzMwOTc->New Members 8
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkdmFxbjQxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDAyNzMzMDk3><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___