You are autosizing the total capacity and volumetric air flow rate.

Where is this DX coil located.... in Zone equipment or in an air loop?

Multiple factors impact the required supply air flow rate and the required cooling capacity.  In this instance, the ratio of autosized capacity to autosized flow rate is slightly outside of the recommended range, as noted in the warning message. 

In your case, the autosized rated cooling capacity was reduced by 120 watts (3%) in order to meet the minimum expected ratio of rated air flow rate to rated capacity.

You might want to look at the Sizing:Zone objects in your project file .. increasing the Design Air Temperature by a small amount (or reducing the "Temperature Difference" by a small amount) may boost the autosized air flow rate slightly... which might removing the warning.



------------------------------------
Posted by: Don Shirey <dshireyiii@xxxxxxxxx>
------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.

------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/