Re: [EnergyPlus_Support] Radiant with DOAS sizing error



HJ

You need to play with a number of parameters in Sizing:System and
Controller:OutdoorAir objects for your DOAS system.

If you size your DOAS on "ventilation" then there will be excess
heating and cooling that cannot be met. You can see this in the HTML
report under unmet hours. But if you changet the sizing to "sensible",
all of the excess heating and cooling will be met by the DOAS.

You need to set the equipment connection to set the priority on
heating and cooling of the zone between the radiant and the DOAS.

If you have big DOAS coils as the result of your autosize calculation,
you need to say "No" to 100% OA when cooling and cooling. With this
setting, you will have DOAS most of the time but when there is extra
heating and cooling beyond the ventilation load, then the OA fraction
will be reduced to meet the load.

Ery


On Tue, 24 Jun 2014, HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support] wrote:

> Hi all,
> 
> I have some projects that has radiant system with DOAS. I find 
> EnergyPlus could not size this type of system properly it never try to 
> meet the thermostat temeprature. When I look at the summer or winter 
> design condition, the temperature could go as high as 30 or as low as 7. 
> I used openstudio to export to EnergyPlus. For radiant system, it does 
> not use thermostat but use its only temperature control, I wonder if 
> that could be the problem for sizing? Does anyone have any successful 
> experience with this type of system sizing and could share your idf file?
> 
> Many thanks,
> 
> HJ



------------------------------------
Posted by: Ery Djunaedy <ery.mailinglist@xxxxxxxxx>
------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.

------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/