|
That was a good reply. This is the "other" kind of DOAS and is far less than typical (at least in Europe). To continue on "my" kind of DOAS...setup the setpoint managers for the AHU to supply air in a range of roughly 18 to 23 deg C. If the minimum outdoor air supplied at these extremes does not pick up the remaining zone loads when the zone equipment can't, then the zone equipment is not effective enough. Zone equipment is sized at air supply temperatures of 22 deg C (sizing:zone object). Another hint for radiant systems: Forget setback temperatures with delta T greater than 2 deg C, i.e. If your heating setpoint is 20 deg C, set your radiant system's schedule to 21 deg C with a throtteling range of 1 (so that the valve is fully open at Tzone 20 C, half open at 21 C and fully closed at 22 C. Then when you setup the setback thermostat to 18, also adjust the radiant system's schedule...and ramp up slowly from 18 to 20. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 25.06.2014, at 18:22, "Ery Djunaedy ery.mailinglist@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |