Biggest tip for radiant systems is to control the surface temperatures. If they are correct, and you still get unmet loads, then you need an additional surface area or auxillary equipment in the zone like a fancoil. The convective and radiative heat transfer is ABSOLUTELY limited by the amount of area at temperature in the active surface. Check with hand calculations what W/m2 you can expect and if it is enough to meet your loads. Side note: Why is your limit of 17 deg C imposed? If outdoors is warm and you need heating inside, you could use warmer air, no? Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 25.06.2014, at 21:17, "HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |