[EnergyPlus_Support] Re: Fan Power Minimum Flow Rate Input Method





Thank you, Jean. I am not able to identify the origin of the problem.

These ones are the objects relative to the fans:

 

Fan:VariableVolume,

    AHU-1 AHU/1 Supply Fan,  !- Name

    occupazione,             !- Availability Schedule Name

    0.70,                    !- Fan Total Efficiency

    512,                     !- Pressure Rise {Pa}

    5.803,                   !- Maximum Flow Rate {m3/s}

    Fraction,                !- Fan Power Minimum Flow Rate Input Method

    0,                       !- Fan Power Minimum Flow Fraction

    0.000000,                !- Fan Power Minimum Air Flow Rate {m3/s}

    0.90,                    !- Motor Efficiency

    1.00,                    !- Motor In Airstream Fraction

    0.0013,                  !- Fan Power Coefficient 1

    0.147,                   !- Fan Power Coefficient 2

    0.9506,                  !- Fan Power Coefficient 3

    -.0998,                  !- Fan Power Coefficient 4

    0.0000000000,            !- Fan Power Coefficient 5

    AHU-1 AHU/1 Cooling Coil Air Outlet Node,  !- Air Inlet Node Name

    AHU-1 Supply Side Outlet 1,  !- Air Outlet Node Name

    General;                 !- End-Use Subcategory

 

Fan:VariableVolume,

    AHU-1 AHU/1 Extract Fan, !- Name

    occupazione,             !- Availability Schedule Name

    0.65,                    !- Fan Total Efficiency

    300,                     !- Pressure Rise {Pa}

    5.803,                   !- Maximum Flow Rate {m3/s}

    Fraction,                !- Fan Power Minimum Flow Rate Input Method

    0,                       !- Fan Power Minimum Flow Fraction

    0.000000,                !- Fan Power Minimum Air Flow Rate {m3/s}

    0.90,                    !- Motor Efficiency

    1.00,                    !- Motor In Airstream Fraction

    0.0013,                  !- Fan Power Coefficient 1

    0.147,                   !- Fan Power Coefficient 2

    0.9506,                  !- Fan Power Coefficient 3

    -.0998,                  !- Fan Power Coefficient 4

    0.0000000000,            !- Fan Power Coefficient 5

    AHU-1 Supply Side Inlet, !- Air Inlet Node Name

    AHU-1 AHU/1 Extract Fan Air Outlet Node,  !- Air Outlet Node Name

    General;                 !- End-Use Subcategory

 

 

And this one is the object relative to the outdoor air control:

 

Controller:OutdoorAir,

    AHU-1 AHU/1  Outdoor Air Controller,  !- Name

    AHU-1 AHU/1 Relief Air Outlet,  !- Relief Air Outlet Node Name

    AHU-1 AHU/1 Extract Fan Air Outlet Node,  !- Return Air Node Name

    AHU-1 AHU/1 Mixed Air Outlet,  !- Mixed Air Node Name

    AHU-1 AHU/1 Outdoor Air Inlet,  !- Actuator Node Name

    3.024,                   !- Minimum Outdoor Air Flow Rate {m3/s}

    3.024,                   !- Maximum Outdoor Air Flow Rate {m3/s}

    NoEconomizer,            !- Economizer Control Type

    ModulateFlow,            !- Economizer Control Action Type

    ,                        !- Economizer Maximum Limit Dry-Bulb Temperature {C}

    ,                        !- Economizer Maximum Limit Enthalpy {J/kg}

    ,                        !- Economizer Maximum Limit Dewpoint Temperature {C}

    ,                        !- Electronic Enthalpy Limit Curve Name

    ,                        !- Economizer Minimum Limit Dry-Bulb Temperature {C}

    NoLockout,               !- Lockout Type

    FixedMinimum,            !- Minimum Limit Type

    occupazione,             !- Minimum Outdoor Air Schedule Name

    ,                        !- Minimum Fraction of Outdoor Air Schedule Name

    occupazione,             !- Maximum Fraction of Outdoor Air Schedule Name

    ,                        !- Mechanical Ventilation Controller Name

    ,                        !- Time of Day Economizer Control Schedule Name

    No,                      !- High Humidity Control

    ,                        !- Humidistat Control Zone Name

    1,                       !- High Humidity Outdoor Air Flow Ratio

    Yes,                     !- Control High Indoor Humidity Based on Outdoor Humidity Ratio

    BypassWhenWithinEconomizerLimits;  !- Heat Recovery Bypass Control Type

 

 

The schedule â??occupazioneâ??, which is relative to the occupation time, is used both in the fans and in the outdoor air control:

 

Schedule:Compact,

    occupazione,             !- Name

    Fraction,                !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For: Weekdays SummerDesignDay WinterDesignDay,  !- Field 2

    Until: 14:45,            !- Field 3

    0,                       !- Field 4

    Until: 18:30,            !- Field 5

    1,                       !- Field 6

    Until: 24:00,            !- Field 7

    0,                       !- Field 8

    For: AllOtherDays,       !- Field 9

    Until: 24:00,            !- Field 10

    0;                       !- Field 11

 

In the model there is no SetpointManger:MixedAir object.

 

Here the result relative to the outdoor air flow rate during the summer season:

http://oi57.tinypic.com/9vce95.jpg

 

In the graph the air flow rate that I imposed in Controller:OutdoorAir, i.e. 3.024 m3/s, is never achieved.

In the .eso file during the winter season the outdoor air flow rate is even equal to 0.

What shall I check to solve the problem? What could limit the outdoor air flow rate?

 

Best Regards

Francesco



__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___