Thank you, Jean. I am not able to identify the origin of the problem.

These ones are the objects relative to the fans:

 

Fan:VariableVolume,

    AHU-1 AHU/1 Supply Fan,  !- Name

    occupazione,             !- Availability Schedule Name

    0.70,                    !- Fan Total Efficiency

    512,                     !- Pressure Rise {Pa}

    5.803,                   !- Maximum Flow Rate {m3/s}

    Fraction,                !- Fan Power Minimum Flow Rate Input Method

    0,                       !- Fan Power Minimum Flow Fraction

    0.000000,                !- Fan Power Minimum Air Flow Rate {m3/s}

    0.90,                    !- Motor Efficiency

    1.00,                    !- Motor In Airstream Fraction

    0.0013,                  !- Fan Power Coefficient 1

    0.147,                   !- Fan Power Coefficient 2

    0.9506,                  !- Fan Power Coefficient 3

    -.0998,                  !- Fan Power Coefficient 4

    0.0000000000,            !- Fan Power Coefficient 5

    AHU-1 AHU/1 Cooling Coil Air Outlet Node,  !- Air Inlet Node Name

    AHU-1 Supply Side Outlet 1,  !- Air Outlet Node Name

    General;                 !- End-Use Subcategory

 

Fan:VariableVolume,

    AHU-1 AHU/1 Extract Fan, !- Name

    occupazione,             !- Availability Schedule Name

    0.65,                    !- Fan Total Efficiency

    300,                     !- Pressure Rise {Pa}

    5.803,                   !- Maximum Flow Rate {m3/s}

    Fraction,                !- Fan Power Minimum Flow Rate Input Method

    0,                       !- Fan Power Minimum Flow Fraction

    0.000000,                !- Fan Power Minimum Air Flow Rate {m3/s}

    0.90,                    !- Motor Efficiency

    1.00,                    !- Motor In Airstream Fraction

    0.0013,                  !- Fan Power Coefficient 1

    0.147,                   !- Fan Power Coefficient 2

    0.9506,                  !- Fan Power Coefficient 3

    -.0998,                  !- Fan Power Coefficient 4

    0.0000000000,            !- Fan Power Coefficient 5

    AHU-1 Supply Side Inlet, !- Air Inlet Node Name

    AHU-1 AHU/1 Extract Fan Air Outlet Node,  !- Air Outlet Node Name

    General;                 !- End-Use Subcategory

 

 

And this one is the object relative to the outdoor air control:

 

Controller:OutdoorAir,

    AHU-1 AHU/1  Outdoor Air Controller,  !- Name

    AHU-1 AHU/1 Relief Air Outlet,  !- Relief Air Outlet Node Name

    AHU-1 AHU/1 Extract Fan Air Outlet Node,  !- Return Air Node Name

    AHU-1 AHU/1 Mixed Air Outlet,  !- Mixed Air Node Name

    AHU-1 AHU/1 Outdoor Air Inlet,  !- Actuator Node Name

    3.024,                   !- Minimum Outdoor Air Flow Rate {m3/s}

    3.024,                   !- Maximum Outdoor Air Flow Rate {m3/s}

    NoEconomizer,            !- Economizer Control Type

    ModulateFlow,            !- Economizer Control Action Type

    ,                        !- Economizer Maximum Limit Dry-Bulb Temperature {C}

    ,                        !- Economizer Maximum Limit Enthalpy {J/kg}

    ,                        !- Economizer Maximum Limit Dewpoint Temperature {C}

    ,                        !- Electronic Enthalpy Limit Curve Name

    ,                        !- Economizer Minimum Limit Dry-Bulb Temperature {C}

    NoLockout,               !- Lockout Type

    FixedMinimum,            !- Minimum Limit Type

    occupazione,             !- Minimum Outdoor Air Schedule Name

    ,                        !- Minimum Fraction of Outdoor Air Schedule Name

    occupazione,             !- Maximum Fraction of Outdoor Air Schedule Name

    ,                        !- Mechanical Ventilation Controller Name

    ,                        !- Time of Day Economizer Control Schedule Name

    No,                      !- High Humidity Control

    ,                        !- Humidistat Control Zone Name

    1,                       !- High Humidity Outdoor Air Flow Ratio

    Yes,                     !- Control High Indoor Humidity Based on Outdoor Humidity Ratio

    BypassWhenWithinEconomizerLimits;  !- Heat Recovery Bypass Control Type

 

 

The schedule â??occupazioneâ??, which is relative to the occupation time, is used both in the fans and in the outdoor air control:

 

Schedule:Compact,

    occupazione,             !- Name

    Fraction,                !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For: Weekdays SummerDesignDay WinterDesignDay,  !- Field 2

    Until: 14:45,            !- Field 3

    0,                       !- Field 4

    Until: 18:30,            !- Field 5

    1,                       !- Field 6

    Until: 24:00,            !- Field 7

    0,                       !- Field 8

    For: AllOtherDays,       !- Field 9

    Until: 24:00,            !- Field 10

    0;                       !- Field 11

 

In the model there is no SetpointManger:MixedAir object.

 

Here the result relative to the outdoor air flow rate during the summer season:

http://oi57.tinypic.com/9vce95.jpg

 

In the graph the air flow rate that I imposed in Controller:OutdoorAir, i.e. 3.024 m3/s, is never achieved.

In the .eso file during the winter season the outdoor air flow rate is even equal to 0.

What shall I check to solve the problem? What could limit the outdoor air flow rate?

 

Best Regards

Francesco



__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___