[EnergyPlus_Support] Fan Power Minimum Flow Rate Input Method





As for the object Fan:VariableVolume I don't understand clearly the meaning of the fields "Fan Power Minimum Flow Fraction" and "Fan Power Minimum Air Flow Rate". 

In the "I/O Reference" I read:


Field: Fan Power Minimum Flow Fraction

The minimum air volumetric flow rate for fan power, specified as a fraction of maximum

system air flow rate. Must be between 0 and 1. Note that this field is only used to calculate

the fan power. This field does not enforce the system air flow rate during simulation. The

default is 0.25.


Does it mean that the "Fan Power Minimum Flow Fraction", in combination with the "power coefficients", determines the fan power at the minimum Flow fraction? How?

I read that "This field does not enforce the system air flow rate during simulation" but in my model if I write 0 as "Fan Power Minimum Flow Fraction" the AHU is not able to supply the outdoor air that I specified in Controller:OutdoorAir (it supplies a lower flow rate), while if I write 1 as "Fan Power Minimum Flow Fraction" the AHU can supply the outdoor air that I want.

Regards



__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___