|
As I understand it, the minimum flow fraction sets the fan to always supply at least the design airflow rate x min airflow fraction (if the availibility is non-zero). As most AHU Frequency converter / motor combinations can throttle down the air flow to a certain amount (about 25%) and then no more. Else, it must switch off completely. If the system does not bring the minimum ODA rates you expect, then I think the problem lies elsewhere. Be careful of which fields have priority in the controller:outdoorair object. Simply leaving previous settings in, the wrong fields can mess it up. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 25.06.2014, at 18:37, "fpasserini.tn@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |