Absolutely correct. The coldest surface in the world doesn't cool if there's not enough of it. Increasing water flowrates does hardly anything if the heatflow bottle neck is the limited surface area. This is not the fault of e+, just physics. Jean
PS the NTU method is used to describe the effectiveness of the heat exchanged between the pipes and the material in which it is embedded. This is acurate enough and not the problem in this case.
Thanks Jean. I finally managed to get the cooling umet hour to 0,
basically just reduce the assumed receptacle load and use higher
cooling setpoint (most unmet hour is during cooling season). seems
to me it mostly related to the surface area i have for the radiant
system. If the surface area is too small, the system could not size
it properly (even if you increase the water flow rate or supply
water temperature). I looked through the engineering reference, and
EnergyPlus treat radiant system as heat exchanger and use NTU method
to calculate heat transfer. So unless we include more surface to
have radiant system, increasing plant size wont change unmet load
hour.
HJ
Most (unlike Ned's floor) radiant heating pipes are
imbedded in the floor, so the heat is conducted to the
outer surface. Ned's pipes convect heat to air (to
increase the convection rate he has added metal fins which
one can clamp around the pipes) which then convects it to
the underside of his floor surface (right?). Then the heat
conducts through the wood floor to the outside surface.
HJ, e+ does not have a hanged radiant hydronic model.
But there is a research project underway which will
hopefully address this short-comming.
Essentially, you can use the embedded pipe model as a
work around, but you have to live with the increased
thermal innertia due to the limit on the thermal
diffusivity. That means slow response times and running
slightly more extreme water temperatures to achive the
correct surface temp. Energy-wise, the dT of the water
remains the same, allbeit more extream, so that impacts
slightly on correct plant energy usage simulation.
I have experimented extensively with this model and can
setup pretty accurate systems. I find autosizing slightly
conservitive most times, but this depends largely on what
pressure drops were thought of as good to use in the
energyplus autosizing routine. Mostly, I do manual sizing,
but I'm an engineer with experience in this area, which I
don't even expect the others in my office have, let alone
other energy modellers. My advise is to get a manufacturer
to size these systems for you and then use those values
for manual sizing.
As I said before (and as Ned also said), check your
surface temps. This is the key to everything.
PS convection coeff calculated by e+ is as expected.
For best results, use the ceiling diffuser model or the
adaptive model.
Mit freundlichen
Grü�en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
Yeah I am conerned this might be the problem
especially you have a carpet on the floor. We use
ceiling radiant system and hang them directly
outside. That could be better but energyplus wont
let you set the radiant system on the outside
surface and they have to be inside one layer of
construction. If i just use a layer with really high
conductivity, energyplus will give me a warning
saying it cannot handle it properly. It would be
really helpful if I could know how the sizing of
radiant system work. The sizing:zone or
sizing:system or sizing:plant does not provide any
information regarding to the radiant system sizing
parameters. I wonder this might results in the
undersizing?
HJ
On 6/26/2014 10:49 AM,
'Edward G. Lyon' eglyon@xxxxxxx
[EnergyPlus_Support] wrote:
Iâ??ll
take a quick shot in the dark based on my
own experience this winter with my home
radiant system. The temperature you are
setting for radiant may be the fluid
temperature (I have used radiant surfaces in
Energy+, but not radiant floor heat
systems). I expected my system to work with
a fluid temperature in the range of 50C.
Good thing I didnâ??t rip out my electric
baseboard, because I couldnâ??t keep the room
warm. My wood floor is too insulation even
with Al heat plates around my Pex pipe. I
found I needed to run 80C fluid to stay
warm. With that temperature, my floor
surface was not much above 32C. I think you
should check the floor surface temperature
that you have. If you are not reaching mid
30â??s, you havenâ??t given the system enough
power.
Ned
Lyon, P.E. (MA, WV)
Staff
Consultant
SIMPSON
GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct
617.285.2162 mobile
781.907.9009 fax
www.sgh.com
Thanks Jean. 17 C is VAV air
temperature reset in winter. In summer,
we use 13C for cooling. In winter, we
dont want to heat the air too much
because there will be core zones that
still need cooling, so we use 17 C.
Also, we dont want to supply air
temperature too high in winter because
radiant system will have direct
radiation to people and they will feel
too hot if we supply air temperature at
30 C. So basically, DOAS can only
provide cooling, and radiant will pick
up the rest of the cooling load in
summer and all the heating load in
winter except the ventilation preheat to
17C from the VAV main heating coil.
I agree there will be a limit posed by
the total surface area of radiant
system. But i tried with E+ example file
and they also have the same problem. I
wonder if they under predict the
convective heat transfer too much so the
air temperature wont go up in winter and
down in summer.
HJ
Biggest tip for
radiant systems is to control the
surface temperatures. If they are
correct, and you still get unmet
loads, then you need an additional
surface area or auxillary
equipment in the zone like a
fancoil. The convective and
radiative heat transfer is
ABSOLUTELY limited by the amount
of area at temperature in the
active surface. Check with hand
calculations what W/m2 you can
expect and if it is enough to meet
your loads.
Why is your
limit of 17 deg C imposed? If
outdoors is warm and you need
heating inside, you could use
warmer air, no?
Mit
freundlichen Grü�en- Sent from
my iPhone (excuse the brevity)
Thanks Ery,
I used sized by ventilation
because I want to use DOAS to
provide ventilation only (at
13-17C all time) and use
radiant system to provide the
rest of heating and cooling. I
also set the priority in
zone:equipment to let DOAS
meet the load first and then
use radiant to meet the rest
of the load. However, there
are still tons of unmet load
hours and the energy also
seems to be higher than using
VAV system alone. I also tried
with radiant system without
DOAS, so I only need to meet
the building load, but still I
have tons of unmet load hours.
Do you have any sample files
that you could share with the
group? I would really
appreciate if you could let us
know how you set the
parameter. Seems like there
are other people having the
same problems too. Maybe I
did something wrong with the
zone:sizing or system:sizing
tab?
Thanks,
HJ
HJ
You need to play with a
number of parameters in
Sizing:System and
Controller:OutdoorAir
objects for your DOAS
system.
If you size your DOAS on
"ventilation" then there
will be excess
heating and cooling that
cannot be met. You can see
this in the HTML
report under unmet hours.
But if you changet the
sizing to "sensible",
all of the excess heating
and cooling will be met by
the DOAS.
You need to set the
equipment connection to
set the priority on
heating and cooling of the
zone between the radiant
and the DOAS.
If you have big DOAS coils
as the result of your
autosize calculation,
you need to say "No" to
100% OA when cooling and
cooling. With this
setting, you will have
DOAS most of the time but
when there is extra
heating and cooling beyond
the ventilation load, then
the OA fraction
will be reduced to meet
the load.
Ery
On Tue, 24 Jun 2014, HJ wanghaojie630@xxxxxxxxx
[EnergyPlus_Support]
wrote:
> Hi all,
>
> I have some projects
that has radiant system
with DOAS. I find
> EnergyPlus could not
size this type of system
properly it never try to
> meet the thermostat
temeprature. When I look
at the summer or winter
> design condition, the
temperature could go as
high as 30 or as low as 7.
> I used openstudio to
export to EnergyPlus. For
radiant system, it does
> not use thermostat
but use its only
temperature control, I
wonder if
> that could be the
problem for sizing? Does
anyone have any successful
> experience with this
type of system sizing and
could share your idf file?
>
> Many thanks,
>
> HJ
__._,_.___
Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|