I have a feeling that an evaporative cooling object is not the best object for a setpoint manager, since the evaporative effect varies dramatically as the inlet humidity / wet bulb varies. I have used the same evap cooling object in some models previously when modeling an M-cycle cooler. In those models, I used the evap object upstream of a mixing box and included it as a part of the OutdoorAirSystem:EquipmentList. I used a Fixed Dry Bulb economizer, but did not try to control the outlet temperature directly as you are doing. Since your application does not sound like a “real world” system, I suspect that you’re doing research. An alternative approach would be to define a DX or chilled water pre-cooling coil with a setpoint manager. If you want to zero the energy, define COP = 10,000 James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Hello. I'm attempting to model an hvac system with the outdoor air intake having temperatures a set number of degrees cooler than the weather file. My current strategy is using the EvaporativeCooler:Direct:ResearchSpecial object with the follow outdoor air setpoint manager. When I check the node temperatures at the inlet and outlet nodes of the cooler, there isn't a temperature difference. I can't figure out what I'm doing wrong. I'd appreciate it if anyone has any ideas. Here's the pertinent text from the idf: !- =========== ALL OBJECTS IN CLASS: EVAPORATIVECOOLER:DIRECT:RESEARCHSPECIAL =========== EvaporativeCooler:Direct:ResearchSpecial, OS:EvaporativeCooler:Direct:ResearchSpecial, !- Name Always On Discrete 1, !- Availability Schedule Name 1, !- Cooler Effectiveness 0, !- Recirculating Water Pump Power Consumption {W} Node 6, !- Air Inlet Node Name Node 38, !- Air Outlet Node Name Node 38, !- Sensor Node Name , !- Water Supply Storage Tank Name 0, !- Drift Loss Fraction 2; !- Blowdown Concentration Ratio !- =========== ALL OBJECTS IN CLASS: SETPOINTMANAGER:FOLLOWOUTDOORAIRTEMPERATURE =========== SetpointManager:FollowOutdoorAirTemperature, Follow Outdoor Air Temperature, !- Name Temperature, !- Control Variable OutdoorAirDryBulb, !- Reference Temperature Type -10, !- Offset Temperature Difference {deltaC} 80, !- Maximum Setpoint Temperature {C} -5, !- Minimum Setpoint Temperature {C} Node 38; !- Setpoint Node or NodeList Name !- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE =========== Output:Variable, Node 38, !- Key Value System Node Temperature, !- Variable Name Hourly; !- Reporting Frequency Output:Variable, Node 6, !- Key Value System Node Temperature, !- Variable Name Hourly; !- Reporting Frequency __._,_.___ Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |