[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] ASHRAE 90.1 Proposed Design





For the LEED certification, the real building must comply with the mandatory provisions. Consider that the responsibility for the mandatory provisions is not of the energy modeler, but of the designers.
For the envelope the mandatory provisions are in paragraph 5.4 and there is no requirement for the max U-values (in fact, U-values are in another paragraph, i.e. par. 5.5, and they are used only for the baseline model). 
For the HVAC plants the mandatory provisions are in paragraph 6.4. Not all HVAC systems are regulated (e.g. in ASHRAE 90.1-2007 the water-to-water heat pumps are not regulated, but they are in ASHRAE 90.1-2010).
If you have the LEED v. 4 BD+C Reference Guide, a Table at page 353 compares the mandatory provisions of ASHRAE 90.1-2007 with ASHRAE 90.1-2010.
Regards


__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___