[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] ASHRAE 90.1 Proposed Design





Thank you very much, Santiago.
But could you please in more detail "The building must also comply with Mandatory provisions (sections x.4), this doesn't mean that the parameters are going to be equal to either Mandatory provisions for Prescriptive requirements."?
If we do not need to change/alter some parameters, how we can comply with .....?
Regards,
Sean


---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <santiagogvelez@...> wrote :

Dear Sean, 
Appendix G PRM method requires you to model proposed design as reflected by design or 'as built'  documents. The building must also comply with Mandatory provisions (sections x.4), this doesn't mean that the parameters are going to be equal to either Mandatory provisions or Prescriptive requirements. 

Cheers,
Santiago.


2014-07-28 7:10 GMT-03:00 seanking.1970@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Dear all,


"The simulation model of the proposed design shall be consistent with the design documents including proper accounting of fenestration and opaque envelope types and area; interior lighting power and controls; HVAC system type, sizes, and controls; and service hot water heating systems and controls."


Some other interpretation says "must be exactly as shown on design drawings/documents" (sorry, cannot find where now).


My question is: do these settings need to be modified in order to comply with the Standard's mandatory provisions and prescriptive requirements (such as envelope U-factors, efficiencies of HVAC systems)? My initial thought was we just need to follow the statements shown in first and second paragraphs above, which implies the settings in proposed design can be arbitrary. It looks like I am wrong.


Anybody is clear with it, please give a direction. Thanks a lot.


Best regards,


Sean




__._,_.___

Posted by: seanking.1970@xxxxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___