How can I determine what the real power demand is ? Enter the real equipment efficiency. Regarding sizing, you can use the sizing parameters object to set an averaging window for sizing. This will average out the startup peaks you see yet still meet the load. In the example below, try using 4, 8, and 12 timesteps for the averaging window (1, 2, and 3 hours) to see what impact that has on sizing and hours set point not met. Timestep,4; Sizing:Parameters, 1.0, !- Heating Sizing Factor 1.0, !- Cooling Sizing Factor ; !- Timesteps in Averaging Window On 8/25/2014 11:52 AM,
geert.bellens@xxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
-- Richard Raustad Senior Research Engineer Florida Solar Energy Center 1679 Clearlake Road Cocoa, FL 32922 Ph: (321)638-1454 http://www.fsec.ucf.edu/en/ Electric Vehicle Transportation Center http://evtc.fsec.ucf.edu/ __._,_.___ Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |