|
Richard,
Thank you for the response, but I've expressed myself in a wrong way I think. I don't want to calculate the consumption, but the 'demand', so efficiency is put at 100% I've noticed that using autosize, sometimes gives me a total heating capacity which is to low. If I manually set a higher capacity, the heating load is met. However, raising the boiler capacity again and again, raises the heat demand at startups, getting higher (but smaller) peaks. These peaks seems to be to high and not realistic. I also see that at startup (in the morning) the floor heating, asks a HVAC heating rate which is sometimes twice as high as expected.... Are these peaks for real? I really can't decide to take these short peaks (neither at zone level or building level) as design load.... Geert
__._,_.___ Posted by: Geert Bellens <geert.bellens@xxxxxxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |