Re: [EnergyPlus_Support] Inserting a Coil:Electric:Heating on a Fancoil





Thank you very much Chandan!
It works!

Best Regards,


2014-09-21 10:57 GMT-04:00 Chandan Sharma chandangsharma@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Felipe,

Yes, this is possible. In the expanded idf, you can schedule the fan coil water heating coil to stay off and add electric baseboard heater in ZoneHVAC:EquipmentList. Also adjust cooling and heating sequence in ZoneHVAC:EquipmentList.

Thanks,
Chandan

On Sun, Sep 21, 2014 at 6:12 PM, felipe@xxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Dear Group,


I need to model a 2 pipe fan coil unit with an electric resistance for heating. I initially modeled it as a HVAC Template:Zone:Fan Coil with a electric boiler and with a with 0W pump power. The LEED reviewer told me that, since energyplus is able to model a electric resistance on a fan coil unit, I should model it as it is. He suggest me to turn off the water heating coil and that I simply insert the Coil:Heating:Electric on a expanded IDF.

 Is that possible? 

Has any of you have tried this before?


Kind Regards,


Felipe Durán





__._,_.___

Posted by: Felipe Duran B-GREEN <felipe@xxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___