[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Doubt About VRF System Warning (Severe)





The HVACTemplate is not copying the inputs for the VRF coil correctly.
In your input file you have specified 3 m3/s cooling and heating flow rate and 55950.76 W capacity for the coils.

  HVACTemplate:Zone:VRF,
    06SUBSOLO:NOBREAK,       !- Zone Name
    3,                       !- Supply Air Flow Rate During Cooling Operation {m3/s}
    3,                       !- Supply Air Flow Rate During Heating Operation {m3/s}
    55950.76,                !- Cooling Coil Gross Rated Total Capacity {W}


Open the Model.expidf file and find this coil, you will see this:

ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Terminal Unit,                     !- Zone Terminal Unit Name
  autosize,                                                !- Supply Air Flow Rate During Cooling Operation {m3/s}
  autosize,                                                !- Supply Air Flow Rate During Heating Operation {m3/s}

Fan:OnOff,
  06SUBSOLO:NOBREAK VRF Supply Fan,                        !- Name
  autosize,                                                !- Maximum Flow Rate {m3/s}

Coil:Cooling:DX:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Cooling Coil,                      !- Name
  Sch_HVAC,                                                !- Availability Schedule Name
  55950.76,                                                !- Gross Rated Total Cooling Capacity {W}
  autosize,                                                !- Gross Rated Sensible Heat Ratio
  autosize,                                                !- Rated Air Flow Rate {m3/s}

Coil:Heating:DX:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Heating Coil,                      !- Name
  Sch_HVAC,                                                !- Availability Schedule Name
  55950.76,                                                !- Gross Rated Heating Capacity {W}
  autosize,                                                !- Rated Air Flow Rate {m3/s}


Correct the inputs that show "autosize" to the values you entered in your input file. Then save that file as Model2.idf and run it.

For example, make these changes:

ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Terminal Unit,                     !- Zone Terminal Unit Name
  3,                                                !- Supply Air Flow Rate During Cooling Operation {m3/s}
  3,                                                !- Supply Air Flow Rate During Heating Operation {m3/s}

Coil:Cooling:DX:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Cooling Coil,                      !- Name
  3,                                                !- Rated Air Flow Rate {m3/s}

Coil:Heating:DX:VariableRefrigerantFlow,
  06SUBSOLO:NOBREAK VRF Heating Coil,                      !- Name
  3,                                                !- Rated Air Flow Rate {m3/s}


Do the same to correct other issues in the expanded file.



On 11/6/2014 5:30 PM, Ivan Mezzacapa ivan_slip@xxxxxxxxxxx [EnergyPlus_Support] wrote:
Hello everyone!

I am having a problem simulating a VRF system. I created the entire system and the simulation shows me an error that makes no sense for me.

Is reporting that i was inserted data that do not conform to the model input. It's the first time I see this error.

 ** Warning ** SizeDXCoil: Coil:Cooling:DX:VariableRefrigerantFlow 06SUBSOLO:NOBREAK VRF COOLING COIL
   **   ~~~   ** ...Rated Total Cooling Capacity will be limited by the maximum rated volume flow per rated total capacity ratio.
   **   ~~~   ** ...DX coil volume flow rate (m3/s) = 3.000000
   **   ~~~   ** ...Requested capacity (W) = 36641.887
   **   ~~~   ** ...Requested flow/capacity ratio (m3/s/W) = 8.187E-005
   **   ~~~   ** ...Maximum flow/capacity ratio (m3/s/W) = 6.041E-005
   **   ~~~   ** ...Adjusted capacity (W) = 49660.652
  
 ************* SizeDxCoil: Potential issue with equipment sizing for Coil:Cooling:DX:VariableRefrigerantFlow 06SUBSOLO:NOBREAK VRF COOLING COIL
   **   ~~~   ** User-Specified Total Cooling Capacity of 55950.76 [W]
   **   ~~~   ** differs from Design Size Total Cooling Capacity of 49660.65 [W]
   **   ~~~   ** This may, or may not, indicate mismatched component sizes.
   **   ~~~   ** Verify that the value entered is intended and is consistent with other components.
 
  ************* SizeVRF: Potential issue with equipment sizing for AirConditioner:VariableRefrigerantFlow 03SUBSOLO:SUPERVISAOPREDIAL VRF TERMINAL UNIT
   **   ~~~   ** User-Specified Rated Total Heating Capacity of 63000.00 [W]
   **   ~~~   ** differs from Design Size Rated Total Heating Capacity of 55950.76 [W]
   **   ~~~   ** This may, or may not, indicate mismatched component sizes.
   **   ~~~   ** Verify that the value entered is intended and is consistent with other components.
  
 ** Warning ** SizeDXCoil: Coil:Cooling:DX:VariableRefrigerantFlow 06SUBSOLO:DADOSEVOZ VRF COOLING COIL
   **   ~~~   ** ...Rated Total Cooling Capacity will be limited by the minimum rated volume flow per rated total capacity ratio.
   **   ~~~   ** ...DX coil volume flow rate (m3/s) = 0.000000
   **   ~~~   ** ...Requested capacity (W) = 0.000
   **   ~~~   ** ...Requested flow/capacity ratio (m3/s/W) = 0.000
   **   ~~~   ** ...Minimum flow/capacity ratio (m3/s/W) = 4.027E-005
   **   ~~~   ** ...Adjusted capacity (W) = 0.000
   ** Severe  ** Sizing: Coil:Cooling:DX:VariableRefrigerantFlow 06SUBSOLO:DADOSEVOZ VRF COOLING COIL has zero rated air flow rate

If anyone can help, I'd be grateful. Follow the idf.

Best regards,

Técg. Ivan Mezzacapa

Projetista  de Ar Condicionado / Consultor em Eficiência Energética


Celular: (11)9963-9326


-- 
Richard Raustad
Senior Research Engineer
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/


__._,_.___

Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___