The HVACTemplate is not copying
the inputs for the VRF coil correctly.
In your input file you have specified 3 m3/s cooling and
heating flow rate and 55950.76 W capacity for the coils.
HVACTemplate:Zone:VRF,
06SUBSOLO:NOBREAK, !- Zone Name
3, !- Supply Air Flow Rate
During Cooling Operation {m3/s}
3, !- Supply Air Flow Rate
During Heating Operation {m3/s}
55950.76, !- Cooling Coil Gross Rated
Total Capacity {W}
Open the Model.expidf file and find this coil, you will
see this:
ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Terminal
Unit, !- Zone Terminal Unit Name
autosize,
!- Supply Air Flow Rate During Cooling Operation {m3/s}
autosize,
!- Supply Air Flow Rate During Heating Operation {m3/s}
Fan:OnOff,
06SUBSOLO:NOBREAK VRF Supply
Fan, !- Name
autosize,
!- Maximum Flow Rate {m3/s}
Coil:Cooling:DX:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Cooling
Coil, !- Name
Sch_HVAC,
!- Availability Schedule Name
55950.76,
!- Gross Rated Total Cooling Capacity {W}
autosize,
!- Gross Rated Sensible Heat Ratio
autosize,
!- Rated Air Flow Rate {m3/s}
Coil:Heating:DX:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Heating
Coil, !- Name
Sch_HVAC,
!- Availability Schedule Name
55950.76,
!- Gross Rated Heating Capacity {W}
autosize,
!- Rated Air Flow Rate {m3/s}
Correct the inputs that show "autosize" to the values
you entered in your input file. Then save that file as
Model2.idf and run it.
For example, make these changes:
ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Terminal
Unit, !- Zone Terminal Unit Name
3, !-
Supply Air Flow Rate During Cooling Operation {m3/s}
3, !-
Supply Air Flow Rate During Heating Operation {m3/s}
Coil:Cooling:DX:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Cooling
Coil, !- Name
3, !-
Rated Air Flow Rate {m3/s}
Coil:Heating:DX:VariableRefrigerantFlow,
06SUBSOLO:NOBREAK VRF Heating
Coil, !- Name
3, !-
Rated Air Flow Rate {m3/s}
Do the same to correct other issues in the expanded
file.
Hello everyone!
I am having a problem simulating a VRF system.
I created the entire system and the simulation
shows me an error that makes no sense for me.
Is reporting that i was inserted data that do
not conform to the model input. It's the first
time I see this error.
** Warning **
SizeDXCoil:
Coil:Cooling:DX:VariableRefrigerantFlow
06SUBSOLO:NOBREAK VRF COOLING COIL
** ~~~ **
...Rated Total Cooling Capacity will be
limited by the maximum rated volume flow per
rated total capacity ratio.
** ~~~ ** ...DX
coil volume flow rate (m3/s) = 3.000000
** ~~~ **
...Requested capacity (W) = 36641.887
** ~~~ **
...Requested flow/capacity ratio (m3/s/W) =
8.187E-005
** ~~~ **
...Maximum flow/capacity ratio (m3/s/W) =
6.041E-005
** ~~~ **
...Adjusted capacity (W) = 49660.652
*************
SizeDxCoil: Potential issue with equipment
sizing for
Coil:Cooling:DX:VariableRefrigerantFlow
06SUBSOLO:NOBREAK VRF COOLING COIL
** ~~~ **
User-Specified Total Cooling Capacity of
55950.76 [W]
** ~~~ **
differs from Design Size Total Cooling
Capacity of 49660.65 [W]
** ~~~ ** This
may, or may not, indicate mismatched component
sizes.
** ~~~ ** Verify
that the value entered is intended and is
consistent with other components.
*************
SizeVRF: Potential issue with equipment sizing
for AirConditioner:VariableRefrigerantFlow
03SUBSOLO:SUPERVISAOPREDIAL VRF TERMINAL UNIT
** ~~~ **
User-Specified Rated Total Heating Capacity of
63000.00 [W]
** ~~~ **
differs from Design Size Rated Total Heating
Capacity of 55950.76 [W]
** ~~~ ** This
may, or may not, indicate mismatched component
sizes.
** ~~~ ** Verify
that the value entered is intended and is
consistent with other components.
** Warning **
SizeDXCoil:
Coil:Cooling:DX:VariableRefrigerantFlow
06SUBSOLO:DADOSEVOZ VRF COOLING COIL
** ~~~ **
...Rated Total Cooling Capacity will be
limited by the minimum rated volume flow per
rated total capacity ratio.
** ~~~ ** ...DX
coil volume flow rate (m3/s) = 0.000000
** ~~~ **
...Requested capacity (W) = 0.000
** ~~~ **
...Requested flow/capacity ratio (m3/s/W) =
0.000
** ~~~ **
...Minimum flow/capacity ratio (m3/s/W) =
4.027E-005
** ~~~ **
...Adjusted capacity (W) = 0.000
** Severe **
Sizing:
Coil:Cooling:DX:VariableRefrigerantFlow
06SUBSOLO:DADOSEVOZ VRF COOLING COIL has zero
rated air flow rate
If anyone can help, I'd be grateful. Follow the
idf.
Best regards,
Técg.
Ivan Mezzacapa