Re: [EnergyPlus_Support] Re: PTHP requires air loop?





If you are modeling someone else's design, then model the equipment they have selected.  For you, that means 60 different water loops.
Perhaps the PTHP is needed for supplemental heating, as you indicate.

On Tue, Nov 11, 2014 at 10:03 AM, hjang35@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 


Thank you for your reply.

Yes, I agree with your comments that there are many thermal zones and boilers more than the building needed.

But, the situation of the building is that all apartment units (each unit 85m2) are equipped with an individual gas boiler (21kW) so that each hot water loop in each apartment unit connects a radiant floor object and a boiler.  As you mentioned, they are listed in ZoneHVAC:EquipmentList for each zone.

 In terms of PTHP, it is mainly used for space cooling in summer and for subsidiary heating in winter.  If the system is only used for cooling, should I choose PTAC ?










--

 

James V Dirkes II, PE, BEMP, LEED AP
The Building Performance Team
1631 Acacia Drive, Grand Rapids, MI 49504
(M) 616 450 8653

The more one does what is good, the freer one becomes. There is no true freedom except in the service of what is good and just.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\BPT Logo 35pct15.png